The earth bond test on a class one appliance should be carried out at 25A for obvious (hopefully) reasons. The problem with using an MFT or a battery powered tester is they can't deliver that current.

Good point. MFT would be less useful for class one stuff. Daz
 
Visual inspection is critical and should be performed before testing: plug, socket, lead, connectors, connections, body of equipment, controls of equipment.
Testing:
Earth continuity (on class I only)
Insulation resistance testing (or protective conductor current / leakage test)
Functional test(s)

Records: extensive: equipment register, test and inspect register, fault register, repair register

Limits:
Earth continuity (R is supply cable cpc resistance)
Equipment and supply cable; <= 0.1 + R Ω
Equipment only; <= 0.1 Ω

Insulation resistance
Class I heating and cooking equipment >= 3kW: >= 0.3 MΩ
Other class I equipment; >= 1.0 MΩ
Class II equipment; >= 2.0 MΩ
Class III equipment; >= 0.250 MΩ

Protective conductor current
Portable hand held class I; <=0.75 mA
Class I heating equipment ; <=0.75 mA (or <=0.75 mA/kW) max 5 mA
Other class I ; <=3.5 mA
Class II; <=0.25 mA
Class III; <=0.50 mA

Frequency of inspection and testing determined by risk assessment, guidance in the COP.
 