I

i=p/u

When pat testing guys do you count socket outlets as an item? As 5 were cracked I replaced 5. But should I charge him for every socket as i plugged socket tester in,Thx
 
Last edited by a moderator:
Since when are socket outlets portable appliances?

Report faulty sockets etc. to the relevant person (duty holder) by all means, but charge em for it;NO
 
Last edited by a moderator:
In the book It shows them damaged if I remember right. But aye il just charrge separately for fixing. Them. Thx
 
Page 26 4.4 says should be replaced so is this part of the service or do we just observ and fix what's broken seperatly
 
Nah, you cant charge him for the sockets you simply use to plug the tester in. I am currently doing a fairly large PAT job in my down time and agreed with the estates manager that if i find damaged sockets i will change them at a cost. I think i charge about £8 per socket replaced as i usually have a few in my bag!
 
Page 26 4.4 says should be replaced so is this part of the service or do we just observ and fix what's broken seperatly
Page 26 4.4 is referring to the requirements of a periodic inspection of the fixed installation.
It only mentions the items that are necessary to undertake safe in service inspection and testing.
I would agree that the sockets ought to be replaced but not as part of your PAT testing only as a separate chargeable issue.
 