thanks a lot everyone for taking the time to explain. You made it very easy to understand. I took a look at the graph in BBB. I understand now why we do a PFC test and why a fuse allows a current until it starts reaching over 100 amps. But there's one thing I don't understand, what if your normal design current is supposed to be over 100 amps? I know it's unlikely but say you have 2 x 10 kw showers, electric hob, etc and other things. I guess this is where diversity comes into play and also the cut off time of the fuse on the graph. But worst case scenario, shouldn't there be fuse greater than 100 amp available? Or is that when you start considering a 3 phase supply?
In a 'normal' domestic installation line current rarely exceeds 100a, even with showers/ovens/electric heating etc it is unlikely that all will be in use at the same time, that is the principle of diversity. Many dwellings run without issues on 60a cutout fuses. Where line current is expected to exceed 100a then 3 phase supplies are used with the load balanced as far as possible over the 3 phases.
 
Got it, thanks a lot, I appreciate everyone passing on their knowledge, I have a much better understanding, still a long way to go :)
 