The inspection came backnas unsatisfactory because of the chrome switches.i do understand your point but surely in the real world, the original installation was indeed intended to be class 2 by design and although not strictly compliant with the current regulations
By removing a potentially hazardous situation and returning it to its original design, from a probable C2 situation to a likely C3, you would be hard pushed for someone to have issue with you doing so, ensuring you include the necessary caveats in the paperwork
I would be happy to proceed with this line under the circumstances that a full circuit rewire is either not practicable and/or not affordable
Rather than just walk away from the issue
Especially when I’m dealing with regular customers that I have a good working relationship with
As is the case with many of the EICRs and CU changes that throws up this issue for me
In most cases i would recommend a rewire as i have on the cert but of course the owners have spent thousands on redecorating & then decided on an EICR.