Doesn't matter. There is a high shock risk should you introduce a derived earth into a true earth (TT) environment. Why can't you TT it?Sorry I should have said it's a storage building not used for livestock. Anybody got any ideas to a solution?
That is a high risk strategy considering TN-C-S is not permitted in farm buildings.
If the power is coming from a transformer up a pole then it will be TT
Or is it easier to sink a new rod to avoid any doubt?
Sorry to bring this back up but I would like thoughts on my plan based on the above advise.
I'm going to bring 3phase PME supply across from main building to metal outbuilding but isolate the earth externally.
This means that I'll be TTing this new supply but what I need advise on is whether I sink a new Rod for this or would it be possible to use the Rod already installed for the current single phase TT supply the building uses (see original post for background info)
Thanks in advance
Yes you're right had time to think about it , thay normally have a earthing mat at the bottom of the pole / transformerNot necessarily, it's perfectly possible to have TNCS or TNS from a pole mounted transformer
You'll need to consider what to do about having the two different earthing systems in installation and so be no further forwards.
Can you not use the structural steel already in place as the electrode in the metal building?Sorry to bring this back up but I would like thoughts on my plan based on the above advise.
I'm going to bring 3phase PME supply across from main building to metal outbuilding but isolate the earth externally.
This means that I'll be TTing this new supply but what I need advise on is whether I sink a new Rod for this or would it be possible to use the Rod already installed for the current single phase TT supply the building uses (see original post for background info)
Thanks in advance
Without seeing it ... May be the original DNO supply required TT installation and at some point DNO did an upgrade and it became PME, but the installation has not been updated to use it as means of earthing (may require new bonding etc).I'm onsite now having a look and it's a strange one to trace to be honest, the supply cable for the TT supply actually comes from underground with a PME sticker at the cutout but no earth block has been supplied - does this mean it has the potential to be a pme system however can't be because of the buildings use and therefore has been TT'd?