Ok, so doing a job and the customer keeps wanting more and more stuff done as time goes on.
Which is a good thing I guess
Anyhoo, they are now wanting a brick shed with lights and a socket. I am already going to intall a new seperate cu for the extension as they don't want the old one touched in case there is more work to be done.
But would the best option be to run some 2core swa from the new cu on a 32A breaker (would this need to be on the RCD side?) then have another cu in the garage for the lights and the socket.
With voltage drop on 50m I calculated 2.5 would be sufficient with a max load avialable being 31.4amps on the cable, more than enough for lights and 1 socket.
Then earth swa at new cu end and leave unconnected at garage cu, then install earth rod for earth in garage.
Which is a good thing I guess

Anyhoo, they are now wanting a brick shed with lights and a socket. I am already going to intall a new seperate cu for the extension as they don't want the old one touched in case there is more work to be done.
But would the best option be to run some 2core swa from the new cu on a 32A breaker (would this need to be on the RCD side?) then have another cu in the garage for the lights and the socket.
With voltage drop on 50m I calculated 2.5 would be sufficient with a max load avialable being 31.4amps on the cable, more than enough for lights and 1 socket.
Then earth swa at new cu end and leave unconnected at garage cu, then install earth rod for earth in garage.
The most recent (from a lecturer) was that the armouring should always be earthed at both ends regardless of what else is going on eg an internal core being used as the cpc (obviously not applying in your case) The answer to this could affect your decision for 1).