Discuss Problems with local DNO in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
17
While doing a few initial tests during a quote for a rewire the ZE results were around the 3 ohm mark on what appeared to be a TNS system. An old iron conduit with two core cable inside and a steel clamp around the intake for the earth.

initially explained to the customer, and got them to contact UKPN. I thought that would be all sorted ready for me to start...

UKPN are now after the second visit saying that it is not a TNS system and they haven’t provided an earth. They are able to change to PME but are unsure at the moment whether this would mean excavation to the road way, or just digging back to below where they have installed an iron intake for the existing cable. Either way, the job would be chargeable (£1000+)and a simple service head change is apparently unavailable.

So it looks like I’ll be converting to TT, which is not a huge issue. However, what would your opinion being on providing a means of earthing via rods. Making sure they are providing suitable Ra. Which I know around me due to chalky ground good is 50-100ohms. However leaving the earth connection to the incoming supply/iron conduit connected, as it has a far superior earth value than what I’ll be able to achieve and both are now effectively extraneous conductive parts?
 

Reply to Problems with local DNO in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
997
So this is 1st floor maisonnette with concrete floor, 16mm2 single insulated tails coming from dual cut out on ground floor, through steel...
Replies
5
Views
857
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Hi All, I have a question trying to understand earthing arrangments SO, We have a DNO Substation, 4 Core armoured Feeding the Distribution Board...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock