OP
daiplayer
earth rod spacing : interesting . earth rod length = space distance . is that apllicable to terraced houses both TT ?
Discuss pro's advice needed in the UK Electrical Forum area at ElectriciansForums.net
Its a TT with a Ze of 207 , ( high i know ) what can i do about this ? inform dno :- convert to TNC-S?
Any way : PEFC : 1.11 a , ( LOW ) PSCC 1.2KA . HIGHEST Zs in house 3.43 , existing bonding 6mm .
As a rule of thumb ive heard of people using 0.5 of main supply tails : 16mm .
However if i inform the DNO of the high Ze and they convert to TNC-S , pefc will rise to eg: 230/0.35 : 657A min.
Any ideas ? or can show me how to do the adiabatic with this ?
Parallel paths with that bonding and all the CPC I would guess be the reason he as got a low Zs there RT
Reply to pro's advice needed in the UK Electrical Forum area at ElectriciansForums.net