Hi,

Whilst it is not best practise, is there any harm in a 10mm G&Y cable running along the outside of a building. The cable is currently tied to existing conduit, (there is no space in the conduit to run additional cable) and is unlikely to encounter any impact in its location. So the only possible concern I can see if that of damage from the elements, however as the cable is on the shaded part of the house, direct sunlight is not an issue, which only leaves temperature. Installing additional conduit in which to house the cable is not doing to safeguard against this? As a guess range of temp is between -5C at to 35C.
Does action need to be taken?
 
A cable run outside should have machanical protection either by getting your cable in some new conduit, getting bigger conduit and putting all cables in or run SWA but at 10MM this might be the most expensice idea.
 
apart from a morbid hatred of T + E clipped direct outside, as you seem to have done a pretty fair risk assessment then no I can't see anything wrong with it.

Being ties to the conduit is dirt rough to leave and I personally would argue your not adhering to regulation 522.8.3.

Could you fit a piece of decent mini trunking to run it in, or even change it for singles or even strip it down, and try and get into the conduit. Must be better ways to achieve installation
 
The OP states its a G/Y cable so I'm assuming it's not T+E. I would however assume the same degree of protection would be desirable as has been described in the above posts. What is the function of this cable ?
 
Hi Malcolm,

Thanks for the response, and I was hoping someone could verify this was ok. I agree with the you that cable clipped direct is abit of an eye sore. Unfortunately mini trunking wouldn't work because of saddle brackets used to hold 20mm conduit up would create obstruction. So new conduit looks like only answer to it. With regards to 522.8.3 there does not appear to be any stress on the cable due to radius of the bends, in this case.
 

Reply to Protecting cables against external factors in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock