P

Piratepete

Hi Guys My Martindale VI 13700G Voltage Indicator has gone walkies. For proving isolation do I have to have a single function voltage tester like the Martindale or could I use a multifunction instrument like the Fluke T5-1000 Electrical Tester (which I want for it's AC current open jaw measuring)? Also - do I have to have a proving unit? Cheers Pete
 
you can use the t5-1000, and for a proving unit, i use the supply i'm working on ( incoming terminals on main switch )
 
There's been a thread on this recently.

A true proving tester shouldn't have batteries, like a Multi or clamp meter.

Personaly I've never had a problem with relying on a battery powered meter using test live, test dead, test live again to prove meter.
 
Hi Guys
You've just forced me to read my copy of GS38 (Feb 1995). Unless it's been revised, clause 17 states that 'a proprietary test lamp or 2-pole voltage detector' is 'preferred' to a multimeter - not obligatory. Also 'a known live source of similar voltage to the circuit under test' may be used for proving. But clause 12 says that 'Instruments used solely for detecting voltage' should have non detachable leads and max 4mm bare probes. Anything else is (not recommended) but is allowed. It's all a bit ambiguous!
I could buy the Fluke T50 as well for a mere £22, it has a captive lead but it hasn't got 4mm probes.
 
Last edited by a moderator:
Hi Guys My Martindale VI 13700G Voltage Indicator has gone walkies. For proving isolation do I have to have a single function voltage tester like the Martindale or could I use a multifunction instrument like the Fluke T5-1000 Electrical Tester (which I want for it's AC current open jaw measuring)? Also - do I have to have a proving unit? Cheers Pete
the T5-600 and the T5-1000 are NOT TO GS38.....an approved voltage indicator (such as a martindale) or the fluke T50-T140 are suitable for doing a safe isolation....together with a KNOWN SOURCE OF SUPPLY....such as a proving unit or the incoming side of a DP/TPN iso....
 
i use a GS38 DI-LOG myself.... its better to have the right equipment to carry out such an important task as a safe isolation rather than just risking it by using unsuitable equipment.....
 
well here we are then. noin-detachable leads and no other functions

31KcK12kCML._AA115_.jpg
 
the T5-600 and the T5-1000 are NOT TO GS38.....an approved voltage indicator (such as a martindale) or the fluke T50-T140 are suitable for doing a safe isolation....together with a KNOWN SOURCE OF SUPPLY....such as a proving unit or the incoming side of a DP/TPN iso....

Why do these comply? They're multifunction and require batteries. I note that the T50 will read volts without batteries - not sure about the T100 range.

Pete
 
the T50-T140 will read voltages throughout the instruments range WITHOUT battery/s....the battery/s are there for the continuity function (belling out)....
 
i use a GS38 DI-LOG myself.... its better to have the right equipment to carry out such an important task as a safe isolation rather than just risking it by using unsuitable equipment.....
I do agree with you - sigh. Just think the Martindale is expensive for what it does. Also trying to keep the number of test instruments I carry around to a minimum! So anything multifunction is useful - if safe in their application.
 
I do agree with you - sigh. Just think the Martindale is expensive for what it does. Also trying to keep the number of test instruments I carry around to a minimum! So anything multifunction is useful - if safe in their application.
well the reason why martindales are specifically mentioned by some firms is they will detect ghost voltages that some other voltage indicators wont pick up.....quite a few times now i have seen folk just waving a neon vaguely over exposed conductive parts and thinking thats safe isolation......crackers really....
 

Reply to Proving Isolation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Today I went to fix a minor loose screw on something and after switching off, etc, got out my Martindale VT12 continuity & voltage tester and...
Replies
3
Views
415
i need to purchase a voltage proving unit - i have seen Megger MPU690, Martindale PD690, and Socket and See SP400, and Fluke but difficult to...
Replies
2
Views
338
At the work place. When proving an 11KV Transformer is Dead. We have HV test sticks. With a function test. Part of the procedure is to function...
Replies
16
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
386
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
735

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock