P

PeterPan27

Main protective bonding conductors are to be verfied by test, which one of the following is the main purpose of verifying suitable connections of these conductors?

1- To confirm they provide a suitable path for earth fault currents to achieve disconnection.

2 - To confirm they provide an actual potential between exposed and extraneous parts at the points of connections.

3 - To confirm they reduce overall values of earth fault loop impedance to enable compliance with BS 76 71

4 - To confirmthey provide a reliable connection between the installations main earthing terminal and means of earthing

Any idea peeps?
 
You'll probably get more assistance if you at least take a stab at the answer and give your reasoning.
 
Main protective bonding conductors are to be verfied by test, which one of the following is the main purpose of verifying suitable connections of these conductors?

1- To confirm they provide a suitable path for earth fault currents to achieve disconnection.

2 - To confirm they provide an actual potential between exposed and extraneous parts at the points of connections.

3 - To confirm they reduce overall values of earth fault loop impedance to enable compliance with BS 76 71

4 - To confirmthey provide a reliable connection between the installations main earthing terminal and means of earthing

Any idea peeps?
 
might be the beer, but i think they're all wrong. i would say that they prevent a potential occuring between exposed and extraneous parts
 
Hi tel matey :)
Just double checked the quetion. its equal not actual

Main protective bonding conductors are to be verfied by test, which one of the following is the main purpose of verifying suitable connections of these conductors?

1- To confirm they provide a suitable path for earth fault currents to achieve disconnection.

2 - To confirm they provide an equal potential between exposed and extraneous parts at the points of connections.

3 - To confirm they reduce overall values of earth fault loop impedance to enable compliance with BS 76 71

4 - To confirmthey provide a reliable connection between the installations main earthing terminal and means of earthing

Any idea peeps?
 
Main protective bonding conductors are not involved with the requirements for automatic disconnection of the supply.
As Tel says they are there to reduce to potential difference between exposed and extraneous conductive parts (and so on) so the answers you give to the question do not cover the reasons for testing the connection.
 
Whoops too slow was writing my post as you posted.!
From my post you can eliminate 1 and 3 as answers, the earthing conductor connects the means of earthing to the MET so....
 
this is defo the city and guilds question

Main protective bonding conductors are to be verfied by test, which one of the following is the main purpose of verifying suitable connections of these conductors?

1- To confirm they provide a suitable path for earth fault currents to achieve disconnection.

2 - To confirm they provide an equal potential between exposed and extraneous parts at the points of connections.

3 - To confirm they reduce overall values of earth fault loop impedance to enable compliance with BS 76 71

4 - To confirmthey provide a reliable connection between the installations main earthing terminal and means of earthing

Any idea peeps?
 
i would say its 2? Main protective bonding conductors are to be verfied by test, which one of the following is the main purpose of verifying suitable connections of these conductors?

1- To confirm they provide a suitable path for earth fault currents to achieve disconnection.

2 - To confirm they provide an equal potential between exposed and extraneous parts at the points of connections.

3 - To confirm they reduce overall values of earth fault loop impedance to enable compliance with BS 76 71

4 - To confirmthey provide a reliable connection between the installations main earthing terminal and means of earthing

Any idea peeps?
 
Another one was

The measurement of continuity of a protective conductor is higher than expected, one possible reason for this is the test?

1- leads resistance has not been subtracted

2 - leads resistance has not been added

3 - leads are too small

4- leads are not double insulated
 
Main protective bonding is connected from the incoming metal service (gas water oil) and from extraneous metalwork (items that could introduce an earth potential into the installation because they are connected to the mass of earth)
to the main earth terminal of the installation.

The purpose of this bonding is to ensure that in the case of a fault to earth where exposed conductive parts could rise to the supply potential, all the conductive parts are connected together by the main bonding so that the potential difference between the parts is minimised.

This then means that if someone were touching,say, a light switch and a water pipe at the same time when the fault occurred then there would be no potential difference between these two parts so the person would not receive a shock.

In your question it is asking why you test the connections. What you are doing there is ensuring that the connections are electrically sound and providing a very low resistance path back to the MET.
The higher the resistance the greater the potential difference would be between exposed and extraneous conductive parts and so a greater risk of electric shock.

- - - Updated - - -

Another one was

The measurement of continuity of a protective conductor is higher than expected, one possible reason for this is the test?

1- leads resistance has not been subtracted

2 - leads resistance has not been added

3 - leads are too small

4- leads are not double insulated
Correct on that one.
 