Peter P,

Learn what extraneous and exposed parts are, and the difference between them. Extraneous parts are commonly metallic water and gas pipes brought into a property underground. They are often not at the same potential as the installation earth/exposed conductive parts, despite both being 'earthed'. Hence the need to 'equalise' the PD.

If the test leads, for whatever reason, are giving a value of say 0.78 ohms this will push the test results out so to speak. You could either deduct the 0.78 from the continuity R2 test result or zero/null the leads prior to the test. The answer you highlighted is correct.
 
Its all part of the EU harmonization.
Drop the real name 'Main Equipotential Bonding' and substitute ' Main protective Bonding' , then include a bit about it not being necessary to supplementary bond but then include a passage about 'if you're not sure then bond it', has proved to be very helpful.

But then, the regs are not supposed to be prescriptive but a design guide.
 