missed a point on kitchen rewire for gas ignition today so last minute i ran a short piece of 6mm from cooker outlet plate to a single socket next to the outlet this sound ok?

32a-----6mm-------ccu-----6mm-----cooker outlet------6mm single------- unswitched socket.
 
can't see any problem there. cable is correctly protected.....
 
missed a point on kitchen rewire for gas ignition today so last minute i ran a short piece of 6mm from cooker outlet plate to a single socket next to the outlet this sound ok?

32a-----6mm-------ccu-----6mm-----cooker outlet------6mm single------- unswitched socket.

It happens to us all for one reason or another

Last time I had the same,I used a dual accessory box,cooker outlet on one side and socket on the other
 
reason for the question was i got pulled up for the 6mm between the outlet and socket as apparently the socket terminals are designed to take 4mm max (never knew this and the 6mm seems to fit quite well)

although cant see a problem replacing it with 4mm couldnt see the point
 
Last edited by a moderator:
Actually if it was a ring with a spur there would be 3x 2.5 so they can obviously accomodate a single 6mm can argue the ---- with him now - thanks chaps
 
I have fitted a 6mm and a 4mm into a socket once when converting an old cooker circuit to a socket radial, snug but do-able.
 
City electrical do socket plates with dual terminals. So much easier when doing a spur. Why oh why they're not more widely available I've no idea.!
 
7671 Big Red book - Page 363.

A piece of 2.5mm2 cable would provide fuse blow protection for a 32a fuse on a radial circuit spured off greater then 4mm2 cable.
 