Hi all
I have just moved in and am in the process of adding some sockets. Am I right in saying that I can add to the circuit regardless of which type of circuit it is as the MCB is a 20a, obviously as long as I'm using 2.5mm t+e not speaker wire etc. I get the issues with RFC where 32a fuse meets a 26a cable but wanted to check if there were any other issues I wasn't aware of. Hope this makes sense and thanks in advance for your time.
 
Yes, you can add to the circuit.
You do need to ensure the Zs for the extended part is low enough for the MCB to operate in the event of a fault.
Also, assuming this is a socket circuit, the extra sockets and possibly the cabling will need RCD protection.
 
I get the issues with RFC where 32a fuse meets a 26a cable
What you will find with a ring final circuit is that standard 2.5mm t&e is not rated to 32A as the idea of a ring is that each cable carries half the current, so no cable will ever be carrying 32A
 
And remember you can only ever have one unfused spur off a ring final circuit
 
Unfused spurs from a ring wired in the same cable as the ring are allowed to run one socket (single or double) or one fused connection unit (FCU). Is that better?? what were you thinking Pete999?
 
Unfused spurs from a ring wired in the same cable as the ring are allowed to run one socket (single or double) or one fused connection unit (FCU). Is that better?? what were you thinking Pete999?
Like I said Barnaby, reading your post you say you can only have 1 nonfused spur from a RFC, when in reality you can take spurs from any where on a RFC, from an existing socket, a JB or the point of connection at the CU, I'm not sure of the exact wording as I don't have BS7671 to hand, but somewhere if my memory is correct the number of non fused spurs must exceed the number of socket outlets on the RFC, nt including spurs, so as an example say you have 10 SOs wired as a RFC then the max number of spurs is 10 SOs, as I said I don't have a copy of the BS so unable to check but I think I'm correct, to be sure you nee to check Appendix 15 regulation 433.1 Appendix 15 is an informative document.
 
There’s no limit Pete.
In fact in the past, some rings were wired with all sockets as spurs for some unknown reason.
I generally refer to these as spider rings.
Bloody nightmare, as you can’t spur off from any of the sockets.
 
Since 1970 it is permitted to have more spurs than sockets on the ring, but it is considered poor practice by many electricians to have too many unfused spurs in a new installation (some think they are bad practice in all cases).
In my experience I have found it a lot more difficult to test rings with lots of spurs if you have insulation faults, for example, as there are connections outside of the basic ring which have to be found etc
 
Since 1970 it is permitted to have more spurs than sockets on the ring, but it is considered poor practice by many electricians to have too many unfused spurs in a new installation (some think they are bad practice in all cases).
In my experience I have found it a lot more difficult to test rings with lots of spurs if you have insulation faults, for example, as there are connections outside of the basic ring which have to be found etc
Thanks for that info Guys, how things change?
 
Yes ok - sorry not to make myself clear. Yes spinlondon you are right. That is what i was trying to say but wasn't very clear about it I admit.
No need to be sorry mate, the regs don't make it easy to explain things , Quite sure you knew what you were on about, my concerns were for the OP as there is no information on his skill set,
 
Of course with older properties, none of the JBs will be maintenance free and will now be covered over with laminate flooring or fitted carpets.
 