rolyberkin

-
Arms
Okay may be a thick question but I have an RCD tripping on 5 x test 180 at 40ms. Pass or fail?

GN3 says must not exceed 40ms
BBB says within 40ms
My tester says computer says no.

To be honest I am recommending it be changed anyway but it will be a call back on a new build for another spark so views appreciated. It is a Lewden 32amp rcbo and they normally trip around 19ms.
 
Okay may be a thick question but I have an RCD tripping on 5 x test 180 at 40ms. Pass or fail?

GN3 says must not exceed 40ms
BBB says within 40ms
My tester says computer says no.

To be honest I am recommending it be changed anyway but it will be a call back on a new build for another spark so views appreciated. It is a Lewden 32amp rcbo and they normally trip around 19ms.
Hi - this is why in maths we've got <=> so we know exactly what's intended. Anyway, I think "within 40ms" should be any number that is not larger than it. So my take is a 40 ms result is a pass, but 40.1 ms would be a fail. This would seem to be in line with GN3 interpretation too.
 
So long as the tester is not showing it tested for 40ms and the RCD had not tripped so that test failed and was stopped at 40ms, but instead the tester was actually showing a time of 40ms for the RCD to trip then I would say this was compliant.
Based on the wording in AMD3 it is compliant, not exceeding 40ms; based on the wording in 18th ed you would just need to increase the test current as it states at or above 5IΔn it must trip within 40ms.
 
Just thinking, there were no loads connected when the testing was done?
On one of my assessments I was testing some Lewden RCBOs and they were way off, 100ms+, because the circuit still had loads connected.
As far as I can tell the trip times when unloaded are consistent at either 19ms or 29ms for almost all Lewden RCBOs I have tested (+-1ms).
 
Just thinking, there were no loads connected when the testing was done?
On one of my assessments I was testing some Lewden RCBOs and they were way off, 100ms+, because the circuit still had loads connected.
As far as I can tell the trip times when unloaded are consistent at either 19ms or 29ms for almost all Lewden RCBOs I have tested (+-1ms).
I would be worried about an RCD that doesn’t trip in the required time when there’s a load.
I wouldn’t want to have to switch everything on a circuit off, just so I can be safe when I mow the lawn.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

rolyberkin

Arms
-
Joined
Location
Chelmsford
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Great Waltham Electrical

Thread Information

Title
RCBO Test data - 40 milliseconds
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
rolyberkin,
Last reply from
Deleted member 26818,
Replies
7
Views
4,666

Advert

Back
Top