Okay may be a thick question but I have an RCD tripping on 5 x test 180 at 40ms. Pass or fail?

GN3 says must not exceed 40ms
BBB says within 40ms
My tester says computer says no.

To be honest I am recommending it be changed anyway but it will be a call back on a new build for another spark so views appreciated. It is a Lewden 32amp rcbo and they normally trip around 19ms.
 
Okay may be a thick question but I have an RCD tripping on 5 x test 180 at 40ms. Pass or fail?

GN3 says must not exceed 40ms
BBB says within 40ms
My tester says computer says no.

To be honest I am recommending it be changed anyway but it will be a call back on a new build for another spark so views appreciated. It is a Lewden 32amp rcbo and they normally trip around 19ms.
Hi - this is why in maths we've got <=> so we know exactly what's intended. Anyway, I think "within 40ms" should be any number that is not larger than it. So my take is a 40 ms result is a pass, but 40.1 ms would be a fail. This would seem to be in line with GN3 interpretation too.
 
So long as the tester is not showing it tested for 40ms and the RCD had not tripped so that test failed and was stopped at 40ms, but instead the tester was actually showing a time of 40ms for the RCD to trip then I would say this was compliant.
Based on the wording in AMD3 it is compliant, not exceeding 40ms; based on the wording in 18th ed you would just need to increase the test current as it states at or above 5IΔn it must trip within 40ms.
 
Just thinking, there were no loads connected when the testing was done?
On one of my assessments I was testing some Lewden RCBOs and they were way off, 100ms+, because the circuit still had loads connected.
As far as I can tell the trip times when unloaded are consistent at either 19ms or 29ms for almost all Lewden RCBOs I have tested (+-1ms).
 
Just thinking, there were no loads connected when the testing was done?
On one of my assessments I was testing some Lewden RCBOs and they were way off, 100ms+, because the circuit still had loads connected.
As far as I can tell the trip times when unloaded are consistent at either 19ms or 29ms for almost all Lewden RCBOs I have tested (+-1ms).
I would be worried about an RCD that doesn’t trip in the required time when there’s a load.
I wouldn’t want to have to switch everything on a circuit off, just so I can be safe when I mow the lawn.
 

Reply to RCBO Test data - 40 milliseconds in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just popped out to a frustrated customer who has had intermittent tripping of a 30mA RCD for years, on average 5 - 10 x p/month. It used to...
Replies
31
Views
4K
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Replies
4
Views
1K
Morning everyone, this is my first post - although i had an account years before that seems to have been lost. Can any of you shed some light...
Replies
24
Views
5K
Hi. I have Metrel MI 3152 multifunctional tester and in the Line, Z auto menu there is a setting for Zlim(Z (LPE),Z (LN)) and it is fixed at...
Replies
11
Views
1K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock