R
RyanF
Hi All,
Ive just got my results through and I failed my first attempt of AM2 exam on the live testing of inspection and testing. I passed everything else just the live testing simply all because I ran out of time that was allowed for the inspection and testing. So Im gonna try and get re booked back in asap.
So live testing let me get this right ( if i am wrong the let me know)
So first stage of live testing is:-
Polarity live:- test between L1- L2 etcc L1-N... L2- E ensure getting 400/230V.
Ze with board FULLY isolated, with permission disconnect the main earthing conductor and test between E to L1, E to L2 and E to L3. Record on test sheet the highest value as Ze. Must comply with tncs earthing arrangement and maximum value permitted. Once test is done reconnect main earth back in.
I can then take this value and work out zs for each circuit.
Zs exactly the same as the Ze test but, earthing conductor is connected. As I want all parrallel paths in circuit for this test. Record on test sheet.
Then onto PFC test first test PEFC
Test between L1- E etc note the highest reading.
PSCC test L1- N etc note the highest reading.
Double highest value on test sheet as PFC.
Rcd testing,
Simply plus in test meter at further point of the ring and test auto 30mA at 1/2, 1 and 5 times. Compare tripping times to bs7671. Record times on test sheet.
Then simply test functional of test switch to ensure rcbo opperates.
Then phase rotation
Simple 3 probe test on incoming side of the isolato to check that the phases are correct and no phases at mixed.
Then functional test on all corcuits and that they operate as they should etc.
Any hints/ links or guidance will be much appreciated!