The only thing I can think of is there would have been a rise on the cpc which caused some down stream rcds/rcbos to trip.Odd, that is much harder to explain.
The only thing I can think of is there would have been a rise on the cpc which caused some down stream rcds/rcbos to trip.Odd, that is much harder to explain.
A bonded pipe touching the foil?The only thing I can think of is there would have been a rise on the cpc which caused some down stream rcds/rcbos to trip.
The cause was someone putting a screw into the stud wall going through the tin foil insulation and catching the tail of phase one, the tin foil insulation must be getting earth through some of the screws that various Dbs are screwed in.A bonded pipe touching the foil?
Well that's a nice case study .... tails behind insulation in a stud wall.The cause was someone putting a screw into the stud wall going through the tin foil insulation and catching the tail of phase one, the tin foil insulation must be getting earth through some of the screws that various Dbs are screwed in.
I’ve altered it since and run both phases + N in surface mounted in some trunking.Well that's a nice case study .... tails behind insulation in a stud wall.
It sounds like someone could have once done a bit better!