Philip657

Hello

When pat testing a RCD extension lead I always test the RCD is working with the test button and with my meter. but in doing so i normally knock the RCD in the consumer unit out. is there anyway to test this without setting all the rcds off ?

Thanks Philip
 
or plug into a non RCD socket if you can find one.
 
Thanks i know i don't need to do a proper test but i like to make sure everything i do is the best i can do and works correctly and feel happier in doing so.

i haven't been able to find a non rcd socket for ages :(
 
You might also want to point out to the client that having an RCD extension lead plugged into a circuit already covered with an RCD will most likley cause nuisance tripping at some point.
Then there's the fact that it's unnecessary and generally considered a bad idea.(by me anyway:p)
 
I know this post is old, but just come along it.

Just wondering is it possible to do a Ramp Test on a RCD Extension Lead?

Thinking about using the isolator (Above) between the socket and RCD Lead and Ramp Test to see the cut out time.

I know its not required but just wondering if it is possible.
 
I just tried the RCD Test using my MI3000 on a RCD Extension Lead and getting a result of <130ms and 0.1v. - failed

I dont understand why I am getting <130ms.

It is a 20M Extension lead.

I am testing it with the Auto setting @ 30mA


Any Ideas anyone?
could it be the length of the cable being the problem?
or have I got the meter set up wrong?
 