Finished up for Christmas now but every year last knockings, just when you think you are on the home straight a teaser throws a spanner in the works. This year said spanner came in the form of a large house with external lighting fed from a remote garage. The offending circuit fed a number of lights on the garage walls,two either side of the large gated entrance,and a number of bollards down the side of the long drive to the house.These are all controlled by a PIR on the garage,an external 2w switch on the garage,and a 2w switch in the house around a 100m distant from the garage.I noted on arrival that a new 30ma RCD main switch DB had been installed in the garage,the client said the lights often tripped the RCD but insisted they had worked ok since the DB change up until recently.It quickly became apparent that the RCD only tripped when the garage 2w switch switched the lights off,switching the lights on,by any other means including the garage switch and they worked fine,switch them off on the garge switch and the RCD tripped every time.
IR testing threw up some low readings,which were rectified fairly quickly,but I could not improve things above 0.7Mohms.Breaking the various legs out to each set of lights gave good readings,mostly 1+mohm....and the 2w cable to the house,a buried swa gave readings >200Mohm.The 0.7mohm overall reading was a result the combined resistances and I'm convinced not an issue.Existing RCD ramped fine,and other circuits in the DB all clear.
Next obvious port of call then was the garage 2W switch..IR tested the 3c to this,clear. Swapped switch for a temp plate switch....RCD still pops on switch off. Connect plate switch direct to JB in garage...RCD holds!...3c to garage 2W is barely 3m long,but partially buried in the brickwork,so this has to be the problem,as bypassing this 3m of cable cures the issue,perhaps there is some hidden damage? Rewire the 3m of cable from JB to ouside switch...reconnect...result?RCD pops every switch off *&%$&&*!!!! Reconnect switch direct into JB eliminating the rewired cable...RCD holds every time.
Ashamed to say after an entire afternoon of frustration I left the job with the issue remaining. Had a think about it that night and decided it had to be some sort of induced voltage/capacitive effect due to the long cable runs.So next day I returned,took the circuit off the DB and fed it from a dedicated 100ma S type RCD with a 6a MCB......no more problems,RCD holds every time.
Thoughts anyone?...I'm still baffled.
IR testing threw up some low readings,which were rectified fairly quickly,but I could not improve things above 0.7Mohms.Breaking the various legs out to each set of lights gave good readings,mostly 1+mohm....and the 2w cable to the house,a buried swa gave readings >200Mohm.The 0.7mohm overall reading was a result the combined resistances and I'm convinced not an issue.Existing RCD ramped fine,and other circuits in the DB all clear.
Next obvious port of call then was the garage 2W switch..IR tested the 3c to this,clear. Swapped switch for a temp plate switch....RCD still pops on switch off. Connect plate switch direct to JB in garage...RCD holds!...3c to garage 2W is barely 3m long,but partially buried in the brickwork,so this has to be the problem,as bypassing this 3m of cable cures the issue,perhaps there is some hidden damage? Rewire the 3m of cable from JB to ouside switch...reconnect...result?RCD pops every switch off *&%$&&*!!!! Reconnect switch direct into JB eliminating the rewired cable...RCD holds every time.
Ashamed to say after an entire afternoon of frustration I left the job with the issue remaining. Had a think about it that night and decided it had to be some sort of induced voltage/capacitive effect due to the long cable runs.So next day I returned,took the circuit off the DB and fed it from a dedicated 100ma S type RCD with a 6a MCB......no more problems,RCD holds every time.
Thoughts anyone?...I'm still baffled.