When i rcd test with my fluke meter it works on some circuits and on the rest it reads 310.0 Ms an wont trip!! Wots up?? Please help!
 
what?

What do you mean it works on some circuits? Stick it into a socket and test on half, 1 and 5 (both cycles) readings that don't comply = change the RCD.
 
More info needed mate? You only need to test the rcd with all loads disconnected (switch mcbs off) at the load terminals of the RCD.
 
try pressing the test button on 1 of the RCDs that won't trip. if it works then, it's probably become sticky as nobody's tested it for donkeys.
 