J JB30 May 10, 2013 #1 When i rcd test with my fluke meter it works on some circuits and on the rest it reads 310.0 Ms an wont trip!! Wots up?? Please help!
When i rcd test with my fluke meter it works on some circuits and on the rest it reads 310.0 Ms an wont trip!! Wots up?? Please help!
M markc123 May 10, 2013 #2 what? What do you mean it works on some circuits? Stick it into a socket and test on half, 1 and 5 (both cycles) readings that don't comply = change the RCD.
what? What do you mean it works on some circuits? Stick it into a socket and test on half, 1 and 5 (both cycles) readings that don't comply = change the RCD.
S somersetsparks May 10, 2013 #3 More info needed mate? You only need to test the rcd with all loads disconnected (switch mcbs off) at the load terminals of the RCD.
More info needed mate? You only need to test the rcd with all loads disconnected (switch mcbs off) at the load terminals of the RCD.
telectrix ~ Mentor Arms May 10, 2013 #4 try pressing the test button on 1 of the RCDs that won't trip. if it works then, it's probably become sticky as nobody's tested it for donkeys.
try pressing the test button on 1 of the RCDs that won't trip. if it works then, it's probably become sticky as nobody's tested it for donkeys.