Disconnecting a cpc when there is a known fault to earth could raise the earthed parts of that circuit (or if you disconnect the main earth, then all exposed and extraneous parts) up to the line voltage which is not a safe thing to do.
I would recommend that if your IR tests are coming back OK and you cannot find the fault by dead testing that you disconnect a circuit entirely (i.e. at least line and neutral) to remove it from the installation. Then if you put a high powered load on another circuit and the RCD does not trip you have disconnected the faulty circuit and can start checking that one in detail.

In this way if a faulty circuit is still present the RCD will limit the risk.
 
Mud slinging aside, if you've done the dead tests in the correct order, you should of discovered the fault before the live tests. Once on a rewire, I discovered a neutral earth fault on a radial and decided to put it to one side for later, to get the other circuits on. Except I didn't and mixed it up with another radial and connected it up. Got to RCD test and wouldn't function, neither would RCD test button. Went back to basics, and discovered my mistake.

Happy hunting:)
 
Have you got an earth clamp meter?

I think you need to check the residual earth loss across the installation and I suspect you have a combination of a N-E fault and cumulative earth leakage from plugged in devices....
 
Yeah sometimes you just don't want to hear the stuff thats already rattling around in yer head

Remember to tell us what the problem is/was when you find it.
I had one (intermittent tripping) last week, three hours it took to discover an external light switch buried in decking, soaking with condensation. Methodical often wins the day!
 
I presume it's a split load board, a crossed neutral would explain the wrong rcd tripping. The test button not working is odd, did it trip out on a 1/2 x IΔn test?
 
Checked the N connections all correct, button I think is what is throwing me of script indicitive of no current but clamp shows equal current in /out, no trip half test
 
A neutral earth fault can prevent the RCD test button tripping the RCD, see my and others previous posts. Don't ask me why, I'm not that clever, others might have the technical reason. From personal experience, but once experienced, its something you remember.
 
In the end it was a new LED hall light I put in before I took the old board out to give my self light to work as there was none there to begin with, I rigged it up from the henly blocks all kosher via a temp fcu,and it was the last thing into the board and this was causing the issue, as I said my plan was to remove the earths in turn till the tripping stopped and it was the culprit, what' the saying assume nothing suspect everything, well I assumed "cos its new it's ok" , all circuits test out great and as it is class 2 I disconnected the earth till scewjobs send a new one, cheers all for insisting I had a N..E fault