Oh and if you're wondering what the problem with C&G was it was that I wrote 60898 which I obviously know is an MCB which was the reason he raised eyebrows when he started seeing RCD times in my test sheet but no rcd's lol. Also I wrote 6mm instead of 16mm for my earthing conductor. Teaches me for rushing really.

This is the info I was looking for!! Lol so it's not 61008 then as its a split board.. I've only even put 1 of these split boards in I only work on industrial and commercial jobs.

So the main switch will be BS 60947-3?? Then this will obviously indicate that this is a split rcd board.

I think you are getting yourself confused,
if your main switch is just a 100a double pole switch then its a BSEN60947-3, no Rcd.

If its an RCD main switch it will be aBSEN61008

just because you have put BSEN60947-3 does not tell you it's a split load board or that you have an RCD at all.

if you have a 100aDP switch followed by 1or2 rcd's then your main switch is BSEN60947-3 , however if your main switch also provides the Rcd protection then that will be BSEN61008
 