RCD omission risk assessment

Hi guys does anybody please have a template risk assessment for the omission of RCD protection? Or does anyone know where I may locate one? Many thanks in advance.
 
Hi guys does anybody please have a template risk assessment for the omission of RCD protection? Or does anyone know where I may locate one? Many thanks in advance.
There may be one at one of the electric design companies but there is nothing on here that I could find.
I Suggest you use a simply 5x5 matrix table. You need to specify the relevant Clause No. of BS7671, and state why there is a necessity to depart from the requirement.
Then list the various hazards that an RCD would address and compare how your proposal ensures that you reach the same level of safety or better.

I did start to make one of these up in response to a recent discussion on here but I suffered an stupid accident at home and tore the ligaments in my knee and have been out of work and in pain since, and to be honest I have not felt like doing the RA.

If you like I can send you some worked examples but they will not deal with that subject but will give you an idea.
Email me if you want me to send you anything.
 
As I understand the regs omission RA requires a template from HSE as it is governed by S.I. 19 (off the top of my head would have to look!) and must comply with HSE requirements. This is not a common or garden RA.
 
Let the client do it they are best placed. If someone was to get hurt or killed and the lack of additional rcd protection contributed to it your risk assessment could be used in a court of law with you justifying it.
 
Actually I think that has been removed in the 18th and replaced with appendix 2 item 11 re INDG163 on HSE site
 
Those sites are relevant to employees and public risk. The RA to be done here is a CDM designers risk assessment.

Under the EAWR the client cannot do this unless they are suitably competent to understand and identify the risk and propose the remedial action.

In this case the OP is proposing a departure from BS7671 which is permitted as the OP would be deemed to be a competent designer, however a suitable RA needs to be done and attached to the documentation in accordance with BS7671.
 
If the OP undertakes a RA stating additional rcd protection has been omitted then he needs to satisfy the installation is no less safer than if it was provided. It is likely to be a clear departure from BS7671 and I have no idea why someone would leave themselves wide open by doing so.
 
If the OP undertakes a RA stating additional rcd protection has been omitted then he needs to satisfy the installation is no less safer than if it was provided. It is likely to be a clear departure from BS7671 and I have no idea why someone would leave themselves wide open by doing so.

It is not leaving anyone wide open if done competently. We regularly RA out the requirement for RCD protection and I will happily stand in court and back it.
 
It is likely to be a clear departure from BS7671 and I have no idea why someone would leave themselves wide open by doing so.
I, and many others, in the telecoms sector are having big issues with this at the moment.

Our customers don't want RCD protection on their equipment due to the risk of nuisance tripping and the loss of service to their customers. Not a massive problem to knock of 250,000 internet subscribers in one hit however as a lot of networks are now IP based there is a risk that blue light services could be effected at a critical moment.

It has been suggested that we connect their equipment using hard-wiring however they wish to retain the functionality of socket-outlets as you can send a poorly paid FLM engineer to swap a piece of faulty kit rather than a sparky, it all boils down to cost and ease.

Now these socket-outlets aren't just commando sockets under the floor or high level mounted ones, the requirement for additional protection also applies to any power rails, C13, C19 etc, that my also be installed.

It's a massive can of worms and we're currently losing a lot of work as no one is willing to do the risk assessment.

Removing one line has create a massive headache for us, we used to be able to use the following up until the introduction of the 18th:

(b) for a specific labelled or otherwise suitably identified socket-outlet provided for connection of a particular item of equipment.

These are circuits in secure switch rooms with heavily restricted access, no chance of Doris plugging in her curling tongs or lawn mower, these circuits are for dedicated racks that will be there for the next twenty years.
 
AFAIK where RCD has worked no deaths have been recorded and this gives me pause for thought on RA, just saying.
 
I, and many others, in the telecoms sector are having big issues with this at the moment.

Our customers don't want RCD protection on their equipment due to the risk of nuisance tripping and the loss of service to their customers. Not a massive problem to knock of 250,000 internet subscribers in one hit however as a lot of networks are now IP based there is a risk that blue light services could be effected at a critical moment.

It has been suggested that we connect their equipment using hard-wiring however they wish to retain the functionality of socket-outlets as you can send a poorly paid FLM engineer to swap a piece of faulty kit rather than a sparky, it all boils down to cost and ease.

Now these socket-outlets aren't just commando sockets under the floor or high level mounted ones, the requirement for additional protection also applies to any power rails, C13, C19 etc, that my also be installed.

It's a massive can of worms and we're currently losing a lot of work as no one is willing to do the risk assessment.

Removing one line has create a massive headache for us, we used to be able to use the following up until the introduction of the 18th:

(b) for a specific labelled or otherwise suitably identified socket-outlet provided for connection of a particular item of equipment.

These are circuits in secure switch rooms with heavily restricted access, no chance of Doris plugging in her curling tongs or lawn mower, these circuits are for dedicated racks that will be there for the next twenty years.

Why don’t you guys just do the RA? On one hand you have the risk of loosing 999 service coverage for maybe millions of people or the other the ever so slight, if any risk of a contractor being electrocuted?

I would look at possibly installing T Earth sockets with labels on stating these sockets are for ‘x’ equipment only. Maybe even possibly putting a general use socket adjacent, again suitably labelled saying this is for general use and is RCD protected.

To me it is really quite simple or am I missing something????
 
Why don’t you guys just do the RA? On one hand you have the risk of loosing 999 service coverage for maybe millions of people or the other the ever so slight, if any risk of a contractor being electrocuted?

I would look at possibly installing T Earth sockets with labels on stating these sockets are for ‘x’ equipment only. Maybe even possibly putting a general use socket adjacent, again suitably labelled saying this is for general use and is RCD protected.

To me it is really quite simple or am I missing something????
It boils down to our customers stating they don’t want RCD protection but not willing to state that in a documented risk assessment. If we installed RCD protection then technically we’re in breach of contract and liable for any outage costs and fines that can run into the hundreds of thousands per hour.
 