B
Brightspark2
sorry about the late replys , the joys of bt home hub being out of action for 2 days. Thank you for the replys. Yes they are two rcbos was not thinking when typing. I not sure yet if the tripping is overcurrent or earth leakage as i am not due back on site till monday. I have got a feeling it will be overcurrent though. To clear a few things up there are 5 type b20 amp rcbos. Each one individually supplys a caravan hook up where there are 2 type c 16 amp rcbo, both rcbo are 30ma Should i change the 20 amp Rcbo to time delay?
The first RCBO would need to be time delayed otherwise if they are both 30mA it just depends which device is quicker as to which one will trip first.