Discuss RCD trip time in the UK Electrical Forum area at ElectriciansForums.net
300mSec @ x1. typically see <40mSec.
40mSec. @ x5. typically see <20mSec.
Thank you- these are the values I was looking for.
From what I understand the mechanism does not differentiate between 1x and 5x, both trip around the same time without an inverse curve.
on testing RCDs (in this country) we generally find results of around 30-40mS @ x1, and 10-15mS. @ x5.
the RCD detects imbalance between L and N. the higher the current causing the imbalance, the faster it will trip.
An RCD with BSEN 61008 or 61009 is 300ms @ x1
But the old BS 4293 is 200ms @ x1
I think I am right is saying that, I’m sure if not someone will say,
But you don’t really see any of the old BS numbered rcds anymore, there are some Crabtree C50 Rccb about mainly schools,
Here are the results from a BS 4293 I tested today and a picture of the device in question.
similarto a MCB, the higher the current , the faster it trips.
Never knew that. Thanks :) How does the science work for RCDs?
RCDs work by sensing a difference on current flow between L and N ( in your case hot and N). close to the threshold, they trip, as they see an imbalance., i.e when the current i 1 of the conductors leaks to earth (ground) in the event of a fault. the test button simulates earth leakage by putting a resistance across L and E.
@Andy78: Big thanks, I needed that. How much does a tester like that cost?
This is a link to a site sponsor doing a good deal on these type of testers.
Hope it helps you.
That's a multifunction tester, also known as an installation tester, that performs all the tests required to verify safety.
That particular model is about £500 new. It's quite a basic model compared to some. Across all brands they range from about £400 to over £1000 depending on what features are included.
You can get dedicated RCD testers which are a bit cheaper.
[/QUOTE]
Might just get one. Are the cheap ones good? How will the tester tolerate 120 volts and line-line 230 volts?
You would have to look at the details in the specs or contact the seller/manufacturer to find out.
I think some of them do work on those kind of voltages but can't say for certain.
Reply to RCD trip time in the UK Electrical Forum area at ElectriciansForums.net
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
This for an apprentice 32 amp mcb /63amp RCD 1) no power to the sockets 2) installation resistance all good. 3) contunuty good. 4) no loses...