I remember and still have an MK plug top with lamp holder and pygmy lamp. One live wire to the plug and lamp holder the other just to the lamp holder. Plug in and touch the floating wire to the socket cover screw, if it lit polarity and earth all good.
 
Cookie RCDs have a transformer built in the RCD which detect voltage leaking. Does that explain it better

They do incorporate a transformer, but that's not how an RCD works.
Voltage doesn't leak, it can't, voltage is a measure of the energy difference between two points.
Current flows, and can 'leak', but an RCD does not detect leakage (not directly).

An RCD (single phase version) has two transformer coils wound around a common core, one is for the live and the other for the neutral. There is a third coil around the same core which operates the tripping mechanism.
If the current flowing through the live coil is equal to the current flowing through the neutral then they are balanced and the cancel out and no current is induced in the tripping coil.
If a more current flows through one coil than the other then they are not balanced and a current is induced in the tripping coil and the RCD trips.
So an RCD detects an imbalance of current between live and neutral.
It doesn't matter why there is an imbalance, it could be leakage, someone receiving and electric shock, a caoacitir charging, incorrect wiring, short circuit etc etc.
[automerge]1575153013[/automerge]
I know how they work, they use a differential coil to sum zero sequence currents. The thing is I don't exactly get how eletrmechanical RCDs respond faster to high current ground fault vs low current ground faults.

I don't know how many RCDs are purely electromechanical these days, I think a lot of them incorporate some electronics.
This probably has something to do with the faster reaction to higher fault currents.
 
I remember and still have an MK plug top with lamp holder and pygmy lamp. One live wire to the plug and lamp holder the other just to the lamp holder. Plug in and touch the floating wire to the socket cover screw, if it lit polarity and earth all good.

I'd like to point out that it was Westy that said 'plug top' this time.
 
My understanding is the EM RCDs use a magnet resting against a metal electromagnet, that when current flows it cancels the field from the magnet and it lets go triggering the trip mechanism.
 
My understanding is the EM RCDs use a magnet resting against a metal electromagnet, that when current flows it cancels the field from the magnet and it lets go triggering the trip mechanism.
Cookie you are putting to much science into RCD or GFCI breakers. My question is what does it matter how fast it trips. In the US if it sees 30ma leaking it trips. No we don’t do all the testing that the UK does because if it don’t trip or trip fast enough all you can do is buy another one. Let’s pick another topic to discuss it
 
Cookie you are putting to much science into RCD or GFCI breakers. My question is what does it matter how fast it trips. In the US if it sees 30ma leaking it trips. No we don’t do all the testing that the UK does because if it don’t trip or trip fast enough all you can do is buy another one. Let’s pick another topic to discuss it

How do you know if it is tripping correctly without doing the sequence of tests though?
 
How do you know if it is tripping correctly without doing the sequence of tests though?
DPG honestly we don’t test them, how do y’all test them ? We are not required to but I’ve got my continuing education class Saturday to renew my license and I’m going to ask the instructor, so I guess I’ll have an answer next week. The only way I would trip them and make sure they reset. I’ve been on this forum since June and y’all have to test everything. We get accused of bang testing but if I wire something I can guarantee you it will work properly and I can’t speak for the dumb asses who think their (electricians) but couldn’t stick their finger up there but without a map
 
DPG honestly we don’t test them, how do y’all test them ? We are not required to but I’ve got my continuing education class Saturday to renew my license and I’m going to ask the instructor, so I guess I’ll have an answer next week. The only way I would trip them and make sure they reset. I’ve been on this forum since June and y’all have to test everything. We get accused of bang testing but if I wire something I can guarantee you it will work properly and I can’t speak for the dumb asses who think their (electricians) but couldn’t stick their finger up there but without a map

We test the by applying a test current to them with a meter that records the time they take to trip in ms. We are essentially testing that they comply with the product standard they have been built to.

An example of this test, or at least the results of it, I have posted in post#8, and the resource I posted in post #28 describes test procedure and requirements quite well.
 
We test the by applying a test current to them with a meter that records the time they take to trip in ms. We are essentially testing that they comply with the product standard they have been built to.

An example of this test, or at least the results of it, I have posted in post#8, and the resource I posted in post #28 describes test procedure and requirements quite well.
Andy to my knowledge I’ve never seen one and thanks for the info
 
Not since the days of VOELCBs! The test button uses a resistor to link the incoming L to the outgoing N to create an imbalance.
i stand corrected. :mad:
 
Still nice to know the timing and how to test them need be. Yes testing is frowned upon on US forums.
 
Still nice to know the timing and how to test them need be. Yes testing is frowned upon on US forums.
Testing is not frowned upon in the US were just not required to do all the testing that UK has to do. But we have inspectors that come and check our work
 