B Bradley6969 - Jan 8, 2019 #1 40A 30ma RCD tripping out at 22.5ma, would people say that’s low and acceptable as I’d say it was a bit low should be more like 28ma?
Risteard - Arms Supporter Jan 8, 2019 #2 Anything above 15mA and below 30mA is acceptable for a 30mA RCD. Upvote 0 Downvote
D Deleted member 26818 Jan 8, 2019 #3 Split the circuit so the earth leakage is less. Upvote 0 Downvote
O Octopus Jan 8, 2019 #4 Bradley6969 said: 40A 30ma RCD tripping out at 22.5ma, would people say that’s low and acceptable as I’d say it was a bit low should be more like 28ma? Click to expand... Very normal reading in my experience...... Upvote 0 Downvote
D Dicky Woollard - Jan 18, 2019 #5 Bradley6969 said: 40A 30ma RCD tripping out at 22.5ma, would people say that’s low and acceptable as I’d say it was a bit low should be more like 28ma? Click to expand... Upvote 0 Downvote
D Dicky Woollard - Jan 18, 2019 #6 RCD's are compliant of they operate at between 50% and 100% of their rated current. A 30mA RCD can trip at 15mA and be acceptable. Upvote 0 Downvote
Risteard - Arms Supporter Jan 18, 2019 #7 Dicky Woollard said: RCD's are compliant of they operate at between 50% and 100% of their rated current. A 30mA RCD can trip at 15mA and be acceptable. Click to expand... Actually, it MUST NOT operate at 15mA, but anything above it is fine so long as it is less than or equal to 30mA. Upvote 0 Downvote