You still need to check if two MCBs need to be off the make the sockets dead.
I just realized that if one leg is swapped with the ring circuit ones then if i tur off the mcb with two lives i still should shut down at least some sockets. I must check all sockets tonight instead of just 6 of i think 9. And if i still have power on all sockets then it cant be the legs that are switched off.
All sockets have power everywhere so it cant be a matter of live wires being swapped.
I also noticed the problematic circuit lives are marked with black pen. One horizontal line and then two.
What does this mean?
( The attached file wont show)
Just indicates which circuits the cables belong to. I assume in this case for that reason and not to identify the legs of the ring circuits which also why it is done, the reason I assume it was not done for the legs is the single cable has a marking and same markings have been put together. The fact you have issues with isolating the circuits points to an identification mix up.
If no mark is one circuit, 1 mark is the second circuit and 2 marks is the 3rd circuit of that trio of circuits then it is wired correctly to the markings but it would appear there was some mix up perhaps and cables were wrongly marked.
As pointed out by others you really need the correct test equipment to sort this it might also be two issues combined, not actual ring circuits, rings within rings or interconnects between rings as well as mixed up connections at the board.
It requires testing fully to make sure you have rings where you should and no interconnects etc.
I might have to look for honest electritian but i will try a few more days with advice from my father to see what has been done.
By the way i touched neutral and earth after turning off all three mcbs and rcd indeed tripped.
After turning off the general MCB thr rcd didnt trip at all.
Can you view image
If not here uploaded
Which part of Scotland?
I am surprised you can’t find an “honest” electrician.
Ps, images workaround. Use the “insert image” above text box rather than “attach file” below.
I am not. I imagine price is a factor but i think my best effort surpaces any professional i call.
Parcig responce failed.
Will try screenshot. Only inserting links to image upload elsewhere works05-28-14-23-00-47-6012fa4d4ddec268fc5c7112cbb265e7.jpg
After spending 40 minutes on the phone with my father and considering all knowledge I had received here we have managed to separate the circuits and now they turn off their respective circuits. Now I can turn off the living room which turned out to be the linear circuit and the kitchen ring circuit.
I wish to tank everyone who helped me understand whats going on.
By the way my father said after i measured a fluhuating 1.04 to 0.4 volts difference between earth and neutral that that indicates poor grid.
I also understood why even if i shut down the second mcb have power to all sockets. Its because continuinity was maintained in the connection above
To isolate, you need to turn off both live wires, i.e. line and neutral, and a single width MCB only turns off the line, so it does not isolate. Some RCBOs do isolate, but rare for an MCB to isolate.
The RCD looks for an imbalance, the old ELCB measured the bonded earth voltage against true earth, but this could be made inoperative by any rouge connection bonded earth to true earth so they were banned.
Hi i am modernizing the single sockets in the living room and so i started to flip the breakers which says ground floor sockets. To my surprise i still had electricity everywhere on all floors! Thank God I checked.
Then I flipped the other breaker which was labeled kitchen sockets. That did the job as there was no electricity anymore on the ground floor on all sockets including the kitchen.
But then wife yelled she had no power upstairs. As i checked the RCD for all 3 breakers had flipped. Upon testing I discovered that when i flip the first two breakers the RCD trips.
Whats going on???!! What could be the possible wiring that can cause this? Thats the quality of working class homes in uk.
Edit: I tested some more today and now rcd does not trip but if i turn off the breakers and touch the isolated sockets live and neutral wires the rcd trips...so it must have tripped before even the curcuit was isolated. So it wasnt isolated till upstairs sockets were also off. What to make of all this? At the board the socket circuits are two rings and one linear if number of wires are indication
It could be certain floors in the house have too much electricity so you might want to wear a hat in those rooms