Discuss RCD won’t trip help needed in the UK Electrical Forum area at ElectriciansForums.net
TT system, have upfront 60947-2 with added on 61008 with mA and ms settings, now I’m getting Zdb of 22.9 ohms and Ka of 4.0, now the RCD can be what ever I set it to but I’m struggling, I’ve set it to 300ma and 300ms but can’t seem to get it to trip? I also have a split phase supply so have L1 and L3 and N but can’t trip on either phase thanks
Long shot but have you tried the manual trip on the RCD. I have found a few times that because no one has ever tested with the manual button the RCD sticks and you have to switch it off and on before the manual works let alone test current on the circuit.
Yes mate, all ok the RCD I have has a green LED light to show RCD function is on, thanks anyway and it’s brand new
I have another lad coming tomorrow with a different tester and I have a Martindale ET4000 and yes tester will not give a reading above 300ms flashes red but surely the RCD should trip within 300ms x1 to comply?
That’s an additional 300mS to the tripping time the RCD normally has.
Reply to RCD won’t trip help needed in the UK Electrical Forum area at ElectriciansForums.net
Evening all, I have a little conundrum I need to get resolved. I’ve moved an EV charger from a single phase board that was on a 40a breaker and...
Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
14K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Hey all, I’m an electricians mate, trying to get fully qualified but struggling. I’ve got my L3 diploma (C&G 8202-30) and 18th edition, I have...