Justsome Facts . 2394 : Do we Need a Reason . ??
An- Unfused-spur . - Cable-branch of a 30A or 32A . ring-final-circuit . supplying 13A - (Accessories to BS-1363 ) may be wired with . thermoplastic - ( PVC ) or thermosetting-insulated-copper . Line andNeutral-conductor(s) as small as 2.5mm[SUP]2 [/SUP]. as is the casefor the ring-itself - Regulation - 433.1. refer .
2349:- Installerswill recognise that the . Current-Carrying-Capacity . of 2.5mm[SUP]2 [/SUP] thermoplastic-insulated-conductor(s)is . generally less than the . 30A or 32A rated-current of the . fuse orcircuit-breaker . of the ring-circuit . depending on the ( Cable ) installation--method & the Ambient-temperature . Etc
The. same is true for 2.5mm[SUP]2 [/SUP]. thermosetting-insulated-conductor(s) such as in . 6242B - cable where operated at a conductor-temperature . not Exceeding 70°C as isusually necessary to suit the ( Temperature-rating-of-Accessories ) ◄◄
Consequently. the circuit-protective-device . cannot protect the . Unfused-spur-cable. against . ( Overload-current ) Thus. if the spur-cable becomes Overloaded .damage may be caused to the ( Insulation . Sheath . Surroundings of the Cable) or to connected-Accessories . due to the . temperature of the . conductors of the cable rising to above theirrated-value - such as 70°C . forthermoplastic-insulated-cables .
Ring-final-circuit.
2394: Why is a 2.5mm[SUP]2 [/SUP] conductor-size-allowed .
Thequestion therefore arises of why is it permittedto use 2.5mm[SUP]2 [/SUP] thermoplastic-insulated . Line &Neutral-conductors to wire an . Unfused-spur .
Theanswer mainly lies in . condition (b) of the following . three-conditions that apply tothe wiring of a . ring-final-circuit .
(a). The Current-Carrying-Capacity - (Iz ) of the circuit-cable . includingthat in any . unfused-spur . must be not less than - 20A . taking into account the conditions of -Ambient-temperature . grouping & thermal-insulation . along the cable-run - Regulation - 433.1.5. refer .
(b) . The circuit must be designed such that the .load-current . in any part of the circuit . including - Unfused-spurs . is unlikelyto exceed the Current-Carrying-Capacity ofcable for long-periods - typically . ( 1 / hour ) under the intended-conditionsof use - Regulations - 433.1.5. refers .
(c). A conductor -size-larger than . 2.5mm[SUP]2 [/SUP] may berequired for reasons of . ( Vd ) -voltage-drop . Section - 525 refers .
Note : for an . Unfused-spur . compliance with . condition(b) leads to compliance with indent (ii) of . Regulation- 433.3.1. . This allows the . Omission of protection against . Overload for the .Spur-cable . on the basis that the .characteristic of the load on that cableare such that its conductor(s) are unlikely to carry-overload-current’s .
Sofar as an . Unfused-spurcable . is connected . condition(b) willgenerally be met by . designing the installation so that conditions (1) and (2) below are both met .
(1) . The spur-feeds-only.
-One-single or one twin 13A - socket-outlet .
- Oneitem of . fixed-equipment , supplied through a fused-connection-unit .
- More than one item of fixed-equipment . eachitem being supplied through a separatefused-connection-unit . provided the total-load . on the spur-cable -taking-into account diversity . does notexceed the . Current-Carrying-Capacity . of the spur-cable .
(2) . Wherenecessary . to avoid to much-load being plugged-into a 13A - socket-outlet supplied through the spur-cable . a sufficient-numberof other - 13A socket-outlets . not suppliedthrough the same spur-cable . are installedin suitable-positions in the vicinity ofthe . socket-outlet .