2394:Basics .
BS-7671:2011: States - Three-fundamental-requirements. for fault-protection by ( ADS ) in a TN - system . ( Exams )
- Protective-Earthing. - Regulation - 411.3.1.1.
- Protective-equipotential-bonding - 411.3.1.2.
-Automatic-disconnection in case of afault - Regulation-Group - 411.3.2.
• Protective-Earthing . - ( All Protective-conductor)
Earthing-arrangements consisting of the ( Means ) of earthing . the ( Earthing-conductor ) & the circuit-protective-conductor(s) connecting the . exposed-conductive-parts tothe ( MET ) must be present . adequately-sized & properly-connected such that their contribution to the . Earth-fault-loop-impedance ( Zs ) is sufficiently-low . ( Circuit-loop-impedance)
• Protective-equipotential-bonding
Main-protective-bonding-conductor(s) . complying with Section - 544 . are required to connect all . Extraneous-conductive-parts . to the ( MET )
• Automatic-disconnection .under-earth-fault-condition(s) isrequired . to provide fault-protection .Automatic-disconnection . can be provided by a suitable . Overcurrent-protective-device . under earth-fault-loop-impedance . is sufficiently-low to satisfy the disconnection-time requirements of BS-2011: or alternatively . by a RCD - residual-current-device. provided the appropriate requirements are Met .
Protective-devices. ( Genetic-Name )
For. fault-protection - Regulation - 411.4.4. . requires one or more . of the following types of protective-devices to be used.
• An Overcurrent-protective-device such as a . Fuse or Circuit-breaker .
• An RCD .
The operating-characteristics of overcurrent-protective-devices . complying with the relevant product-standards are given in p.295. Appendix - 3 .
- The purposeof ( Earthing ) where used for the .protective-purposes . within an installation. ( is to limit the Duration of the voltages )
- In ( Contrast ) the purpose of ( Bonding) is to limit the ( Magnitude of the voltages )
BS-7671:2011: States - Three-fundamental-requirements. for fault-protection by ( ADS ) in a TN - system . ( Exams )
- Protective-Earthing. - Regulation - 411.3.1.1.
- Protective-equipotential-bonding - 411.3.1.2.
-Automatic-disconnection in case of afault - Regulation-Group - 411.3.2.
• Protective-Earthing . - ( All Protective-conductor)
Earthing-arrangements consisting of the ( Means ) of earthing . the ( Earthing-conductor ) & the circuit-protective-conductor(s) connecting the . exposed-conductive-parts tothe ( MET ) must be present . adequately-sized & properly-connected such that their contribution to the . Earth-fault-loop-impedance ( Zs ) is sufficiently-low . ( Circuit-loop-impedance)
• Protective-equipotential-bonding
Main-protective-bonding-conductor(s) . complying with Section - 544 . are required to connect all . Extraneous-conductive-parts . to the ( MET )
• Automatic-disconnection .under-earth-fault-condition(s) isrequired . to provide fault-protection .Automatic-disconnection . can be provided by a suitable . Overcurrent-protective-device . under earth-fault-loop-impedance . is sufficiently-low to satisfy the disconnection-time requirements of BS-2011: or alternatively . by a RCD - residual-current-device. provided the appropriate requirements are Met .
Protective-devices. ( Genetic-Name )
For. fault-protection - Regulation - 411.4.4. . requires one or more . of the following types of protective-devices to be used.
• An Overcurrent-protective-device such as a . Fuse or Circuit-breaker .
• An RCD .
The operating-characteristics of overcurrent-protective-devices . complying with the relevant product-standards are given in p.295. Appendix - 3 .
- The purposeof ( Earthing ) where used for the .protective-purposes . within an installation. ( is to limit the Duration of the voltages )
- In ( Contrast ) the purpose of ( Bonding) is to limit the ( Magnitude of the voltages )