A
amberleaf
2392-10 / 2394. taken for the main-forum . I do thank my fellow-members for this information . ◄◄
2392-10 / 2394. Please go into the , Main-forum and ask questions . :gettree:
Howdo I work out the following question; When measuring the insulation resistancebetween live conductors of five existing circuits in the installation thefollowing results were obtained.
185Mohms, 150Mohms, 20Mohms, 200Mohms,2.5Mohms
State
a) the value of the installation resistance ifthese circuits were measured as a whole show calculations.
b) whether the value obtained in a)isacceptable
c) which further test would be requiredto complete the insulation resistance testing
d) the minimum acceptablevalue from BS 7671:2008 ( 1MΩ ) table - 61
e) any observations to be made to theclient following the test
1/Rt = 1/R1 + 1/R2 + 1/R3 + 1/R4
1/Rt = 1/185 + 1/150 + 1/20+ 1/200 + 1/2.5
1/Rt = 0.005 + 0.007 + 0.05 + 0.005 + 0.4
1/Rt = 0.467
Rt = 1/0.467
Rt = 2.14 Megohms
Value is acceptable.
c) Insulation-résistance-test betweenlive conductors and earth (cpc)
d) 1Mohm
e) the 2.5 value while acceptable isvery low and would require further investigation if it is a new installation ;if it is an old installation it could be a sign that it is soon going to needrewiring.
2392-10 / 2394. Please go into the , Main-forum and ask questions . :gettree:
Howdo I work out the following question; When measuring the insulation resistancebetween live conductors of five existing circuits in the installation thefollowing results were obtained.
185Mohms, 150Mohms, 20Mohms, 200Mohms,2.5Mohms
State
a) the value of the installation resistance ifthese circuits were measured as a whole show calculations.
b) whether the value obtained in a)isacceptable
c) which further test would be requiredto complete the insulation resistance testing
d) the minimum acceptablevalue from BS 7671:2008 ( 1MΩ ) table - 61
e) any observations to be made to theclient following the test
1/Rt = 1/R1 + 1/R2 + 1/R3 + 1/R4
1/Rt = 1/185 + 1/150 + 1/20+ 1/200 + 1/2.5
1/Rt = 0.005 + 0.007 + 0.05 + 0.005 + 0.4
1/Rt = 0.467
Rt = 1/0.467
Rt = 2.14 Megohms
Value is acceptable.
c) Insulation-résistance-test betweenlive conductors and earth (cpc)
d) 1Mohm
e) the 2.5 value while acceptable isvery low and would require further investigation if it is a new installation ;if it is an old installation it could be a sign that it is soon going to needrewiring.