amberleaf
Initial Verification ,
Order of tests
Order of tests ( Prior ) To the installation being Energized ( After the completion of Inspection )
• Continuity of protective conductors including , main and supplementary bonding 612.2.1.
• Continuity of ring final circuit conductors 612.2.2.
• Insulation résistance 612.3.
• Protection by SELV , PELV or by electrical separation 612.4.
• Basic protection by a barrier or an enclosure provided during erection 612.4.5.
• Polarity .. for example , at lighting switches . 612.6.
• Where the - earth electrode is part of the installation 612.7. “ Earth electrode to Earth shall be measured “
- Alternatively for a TT system the installation earth electrode résistance may be approximately measured with the incoming supply energized and the main switch OFF , using an earth fault loop impedance test instrument .
Order of tests to be carried out with the supply connected
Order of tests
Order of tests ( Prior ) To the installation being Energized ( After the completion of Inspection )
• Continuity of protective conductors including , main and supplementary bonding 612.2.1.
• Continuity of ring final circuit conductors 612.2.2.
• Insulation résistance 612.3.
• Protection by SELV , PELV or by electrical separation 612.4.
• Basic protection by a barrier or an enclosure provided during erection 612.4.5.
• Polarity .. for example , at lighting switches . 612.6.
• Where the - earth electrode is part of the installation 612.7. “ Earth electrode to Earth shall be measured “
- Alternatively for a TT system the installation earth electrode résistance may be approximately measured with the incoming supply energized and the main switch OFF , using an earth fault loop impedance test instrument .
Order of tests to be carried out with the supply connected