A
amberleaf
Re-cap : 2392-10 / 2394 .
Additions & Alterations :icon_bs:
No addition or alteration, temporary orpermanent, shall be made to an existing installation, unless it has beenascertained that the rating and the condition of any existing equipment,including that of the distributor, will be adequate for the altered circumstances.Furthermore, the earthing and bonding arrangements, if necessary for theprotective measure applied for the safety of the addition or alteration, shallbe adequate. 132.16 p20
During erection and oncompletion of an installation or an addition or alteration to an installation,and before it is put into service, appropriate inspection and testing shall becarried out by competent persons to verify that the requirements of theStandard have been met.
Appropriate certificationshall be issued in accordance with Sections 631 and 632. 134.2.1 p22
Upon completion of the verification of anew installation or changes to an existing installation, an ElectricalInstallation Certificate based on the model given in Appendix 6, shall beprovided. Such documentation shall include details of the extent of theinstallation covered by the Certificate, together with a record of theinspection, the results of testing and a recommendation for the interval untilthe first periodic inspection. 631.1 p195
The requirements of Sections 631 and 632for the issue of an Electrical Installation Certificate or a Minor ElectricalInstallation Works Certificate shall apply to all the work of the additions oralterations. 633.1 p196
The contractor or other personresponsible for the new work, or a person authorized to act on their behalf,shall record on the Electrical Installation Certificate or the Minor ElectricalInstallation Works Certificate, any defects found, so far as is reasonablypracticable, in the existing installation. 633.2 p196
Additions & Alterations :icon_bs:
No addition or alteration, temporary orpermanent, shall be made to an existing installation, unless it has beenascertained that the rating and the condition of any existing equipment,including that of the distributor, will be adequate for the altered circumstances.Furthermore, the earthing and bonding arrangements, if necessary for theprotective measure applied for the safety of the addition or alteration, shallbe adequate. 132.16 p20
During erection and oncompletion of an installation or an addition or alteration to an installation,and before it is put into service, appropriate inspection and testing shall becarried out by competent persons to verify that the requirements of theStandard have been met.
Appropriate certificationshall be issued in accordance with Sections 631 and 632. 134.2.1 p22
Upon completion of the verification of anew installation or changes to an existing installation, an ElectricalInstallation Certificate based on the model given in Appendix 6, shall beprovided. Such documentation shall include details of the extent of theinstallation covered by the Certificate, together with a record of theinspection, the results of testing and a recommendation for the interval untilthe first periodic inspection. 631.1 p195
The requirements of Sections 631 and 632for the issue of an Electrical Installation Certificate or a Minor ElectricalInstallation Works Certificate shall apply to all the work of the additions oralterations. 633.1 p196
The contractor or other personresponsible for the new work, or a person authorized to act on their behalf,shall record on the Electrical Installation Certificate or the Minor ElectricalInstallation Works Certificate, any defects found, so far as is reasonablypracticable, in the existing installation. 633.2 p196