Yes this Question has been asked on 2394:
PS . there are still in the Regulations BS-3036 fuse
S1A devices are 1KA. in sizes 5 ,15 , 20 , 30 , 45 , & 60A
S2A devices are 2kA. in sizes 5 ,15 , 20 , 30 , 45 , 60 & 100A
S4A devices are 4kA. in sizes 30, 45, 60 & 100A
Q ) Which of the following protective device is never suitable for determining prospective earth fault current at the origin of an installation
□ BS-3036 fuse
□ BS-88-3 fuse
□ BS-88-2 fuse
□ BS-EN-60898-1 circuit breaker .. 6kA / 10kA .
The maximum breaking capacity of a BS-3036 fuse is 4kA , so it is not a suitable protective device where the fault current is 10kA .
• Note : that the devices are available in three types relating to short-circuit capacity, i.e. 1, 2 & 4kA.
Out but not gone . ?? ... BS-3036 fuse
O.S.G. P/72 .
Regulation 533.1.1.3 of BS-7671:2008 refer
states that a fuse shall preferably be of the cartridge type but this does not preclude the use and installation of semi-enclosed fuses. Where a semi- enclosed fuse is selected, the carrier shall be fitted with an element in accordance with the manufacturer’s instructions,
533.1.1.3 permits the fitting of a single element of tinned copper wire of the appropriate diameter specified in Table 53.1 P/140
Terminology
Those fuses referred to as " rewirable fuses " are correctly termed semi enclosed fuses as they are partially enclosed within the fuse-carrier.
semi-enclosed fuse ... BS-3036 fuse
a fuse in which the fuse element is neither in free air ( other than the air in any external containing case not forming part of the fuse ) nor totally enclosed
Rated breaking capacity
BS-3036 defines breaking capacity as: breaking-capacity rating a prospective current stated by the manufacturer to be the greatest
BS 3036 are suitable in certain applications only.
BS 3036 semi-enclosed fuses cannot be relied upon to operate within 4 hours at 1.45 times the nominal current of the fuse element.
Correct protection can be obtained by modifying the normal condition ( In ≤ Iz ) such that the fuse rating does not exceed 1.45 ÷ 2 = 0.725 times the rating of the circuit conductor
For this reason, larger cables may need to be selected where overload protection is provided by semi-enclosed fuses than when it is provided by a cartridge fuse or fuses or circuit-breaker ( Appendix 4 of BS 7671 and Guidance Note 6 give further guidance ). 2008
Fault Current Protection . from my old 16th Edition notes .
The purpose of fault current protection is to disconnect the supply speedily and restrict damage and danger as far as possible .
All parts of an installation must be protected against the highest ( pƒc ) that can be anticipated at any particular point in the system The ( pƒc ) is at is highest at the intake position and will decrease ( or attenuate ) through the installation as the résistance of cables is added to the fault part .
Short Circuit Rating : Under short-circuit conditions there will be a considerable current surge . This is the ( pƒc ) .. for a standard 100A supply the ( PFC ) often quoted by DNO is 16 000A ( kA ) The value is never as high as that .
much depends upon the arrangement of the supply network and the distance from the substation
Rated short-circuit capacity ( Icn ) of the circuit breaker conforming to BS-EN-60898-1 is the value of the ultimate short circuit breaking capacity assigned by the manufacture .
circuit breaker also has a corresponding " in-service " short circuit breaking capacity ( Ics ) which is either equal to , or lower than , the rated short circuit capacity ( Icn )
Conveniently , ( Icn & Ics ) are the same value for circuit breakers conforming to BS-EN-60898 having an ultimate short-circuit capacity of ( 6kA ) or Less .
PS . there are still in the Regulations BS-3036 fuse
S1A devices are 1KA. in sizes 5 ,15 , 20 , 30 , 45 , & 60A
S2A devices are 2kA. in sizes 5 ,15 , 20 , 30 , 45 , 60 & 100A
S4A devices are 4kA. in sizes 30, 45, 60 & 100A
Q ) Which of the following protective device is never suitable for determining prospective earth fault current at the origin of an installation
□ BS-3036 fuse
□ BS-88-3 fuse
□ BS-88-2 fuse
□ BS-EN-60898-1 circuit breaker .. 6kA / 10kA .
The maximum breaking capacity of a BS-3036 fuse is 4kA , so it is not a suitable protective device where the fault current is 10kA .
• Note : that the devices are available in three types relating to short-circuit capacity, i.e. 1, 2 & 4kA.
Out but not gone . ?? ... BS-3036 fuse
O.S.G. P/72 .
Regulation 533.1.1.3 of BS-7671:2008 refer
states that a fuse shall preferably be of the cartridge type but this does not preclude the use and installation of semi-enclosed fuses. Where a semi- enclosed fuse is selected, the carrier shall be fitted with an element in accordance with the manufacturer’s instructions,
533.1.1.3 permits the fitting of a single element of tinned copper wire of the appropriate diameter specified in Table 53.1 P/140
Terminology
Those fuses referred to as " rewirable fuses " are correctly termed semi enclosed fuses as they are partially enclosed within the fuse-carrier.
semi-enclosed fuse ... BS-3036 fuse
a fuse in which the fuse element is neither in free air ( other than the air in any external containing case not forming part of the fuse ) nor totally enclosed
Rated breaking capacity
BS-3036 defines breaking capacity as: breaking-capacity rating a prospective current stated by the manufacturer to be the greatest
BS 3036 are suitable in certain applications only.
BS 3036 semi-enclosed fuses cannot be relied upon to operate within 4 hours at 1.45 times the nominal current of the fuse element.
Correct protection can be obtained by modifying the normal condition ( In ≤ Iz ) such that the fuse rating does not exceed 1.45 ÷ 2 = 0.725 times the rating of the circuit conductor
For this reason, larger cables may need to be selected where overload protection is provided by semi-enclosed fuses than when it is provided by a cartridge fuse or fuses or circuit-breaker ( Appendix 4 of BS 7671 and Guidance Note 6 give further guidance ). 2008
Fault Current Protection . from my old 16th Edition notes .
The purpose of fault current protection is to disconnect the supply speedily and restrict damage and danger as far as possible .
All parts of an installation must be protected against the highest ( pƒc ) that can be anticipated at any particular point in the system The ( pƒc ) is at is highest at the intake position and will decrease ( or attenuate ) through the installation as the résistance of cables is added to the fault part .
Short Circuit Rating : Under short-circuit conditions there will be a considerable current surge . This is the ( pƒc ) .. for a standard 100A supply the ( PFC ) often quoted by DNO is 16 000A ( kA ) The value is never as high as that .
much depends upon the arrangement of the supply network and the distance from the substation
Rated short-circuit capacity ( Icn ) of the circuit breaker conforming to BS-EN-60898-1 is the value of the ultimate short circuit breaking capacity assigned by the manufacture .
circuit breaker also has a corresponding " in-service " short circuit breaking capacity ( Ics ) which is either equal to , or lower than , the rated short circuit capacity ( Icn )
Conveniently , ( Icn & Ics ) are the same value for circuit breakers conforming to BS-EN-60898 having an ultimate short-circuit capacity of ( 6kA ) or Less .