P

Piratepete

Hi
I note that on the new 'Generic Scedule of Test Results' where there use to be a requirement to record 'Ze at origin' and 'PFC' (at origin), it is now 'Zs at DB' and 'Ipf at DB'.

Is there now no requirement to record Ze at Origin? I note that there is still a requirement to test Ze.

Pete
 
Last edited by a moderator:
What ''Generic Scedule'' are you referring too?? There is always a requirment to test AND record Ze values!!
 
No, Ze is the external earth fault loop impedance external to the installation. I know guidance note 3 refers to the Zs measured at a distribution board as Zdb but I choose not to.
 
and yes only 1 ze of installation but its when to apply ze zs or zdb, least i know what im on about lol

Which is more than we do then ...lol!! Cause only Zs, Zdb applies after the main incoming supply point!!
 
in the book pointd out above it does use zs on test sheets as ze..

i know your worth double what i get payed e54, i know but can only say what i know:yes:

- - - Updated - - -

or seen
 
in the book pointd out above it does use zs on test sheets as ze..

i know your worth double what i get payed e54, i know but can only say what i know:yes:

- - - Updated - - -

or seen


Then something is very wrong in that book!! Ze and Zs, are as i said earlier, ...Very different animals!! lol!!
 
I found it! Page 93 of GN3 BS7671:2008 (without amendment). That sort ye out i=p/u lol

The schedule of test results in this version of GN3 does ask for Ze at origin. Stupid. New version is far better.
 
On the generic schedule of test results it does indeed say Zs at DB. This is exactly that... a generic term for the DB you are working on which may or may not be the one at the incomer. On the EIC itself however, you will find a space for the Ze.
 
I find this to be standard though, as all I work is EICR's on factories, large government offices, schools etc. I rarely will be completing an EICR with only one Distribution board. Sometimes its hard to get your point across on the old interwebatron.
 
Piratepete, these pages that you have included from Pg98/99 of GN3 BS7671:2008 (2011) go along with the pages from 104&105 for an EICR(electrical installation condition report) and Pages 94&95 for an EIC (electrical installation certificate).

I think that is where you have been getting confused, hope this helps.
 
test sheets should i say then... but struggling to find where now, maybe im yapping out my beeeeeep!

Zs=Ze + [R1+R2).

So Zs and Ze can't be the same can they? I'm assuming you know what R1 and R2 is all about?
 
On Page 2, Section I - Nature of Supply Parameters...

Oh, b----r! I've always used this box to enter the worst case values - ie 16kA for Ipf and either 0.35, 0.8 or 200 ohms for Ze. The actual measured values I put on the Schedule of Test Results where the boxes used to ask for Ipf and Ze at Origin. Well, I've never been picked up on this in 10 years! Hurray for NICIEC assessments!
 
Hi to get the value of Zs the formula is as follows Ze+(R1+R2) R1 being the phase conductor and R2 being the CPC
 
Ze is the recorded external impedance at the intake of the supply, Zs is the earth fault loop impedance which is the total resitance of Ze PLUS R1 and R2
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Recording Ze
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
23

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
Piratepete,
Last reply from
sparkymalarky,
Replies
23
Views
3,181

Advert

Back
Top