What type of motorised valve and are any other independent switched outputs required from this setup?

If they are standard 2 port central heating type motorised valves and aren't required to provide any other switched outputs then you don't need relays as the internal microswitches will do the job.

Unless this is switching a higher powered pump that the microswitches can't handle?
 
What type of motorised valve and are any other independent switched outputs required from this setup?

If they are standard 2 port central heating type motorised valves and aren't required to provide any other switched outputs then you don't need relays as the internal microswitches will do the job.

Unless this is switching a higher powered pump that the microswitches can't handle?
 
End switches are low voltage and out of the equation.
the problem is I have two separate motorised valves controlled by stats. But only one pump. It’s getting the pump to come on with either valve With no backfeeding.
thanks
 
End switches are low voltage and out of the equation.
the problem is I have two separate motorised valves controlled by stats. But only one pump. It’s getting the pump to come on with either valve With no backfeeding.
thanks

You say everything is 230V and the end switches are low voltage, so what is the problem?

Please could you be a bit more specific about whhat make/model of valve you are using?
 
Controls are from heat pumps and are low voltage. They are not in the equation. I have 2 motorised valves
And two relays and 1 pump. When activating any valve I want to open valve via stat which is no problem. The problem arises a pump has been added and need any one of the valves to operate the pump but I can’t get it thru relays without back feeding
 
1663839653209321916761386961707.jpg

It's a bit rough as I was leaning on a steering wheel... Use a double throw relay with the common connected to the boiler feed.
 
As davesparks has already said, standard motorised valves have built in microswitches, and these switches are volt free. There is no prospect of back feeding from the switch to the circuitry controlling the valve.
 
Appreciate your help it was as simple as each valve controlled a relay with the pump connection out of each on normally open. Thought I had tried this at the beginning but obviously not.
 

Reply to Relay wiring for motorised valves in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top