D Skelton
Mentor
Last week I did a job for forum member joramtor. Link to the original post here: http://www.electriciansforums.co.uk...s-your-area/87967-repair-micc-pyro-cable.html
He had an underground mineral cable that had been severed by the groundworkers so off we went to sort it out for him. The length of cable that was broken was about 50m long and ran between two lamp posts in his driveway. I thought I might put up some photos of the work along with an explanation so that those less experienced with mineral might learn something. Feel free to add to it if you want (I'm sure much flaw picking and critisism will ensue also :D).
First off the customer snipped a piece off and posted it to me so that I could determine whether it was imperial or metric and also so that I could size the pots and glands needed if it was imperial (the job was over an hour away so couldn't just pop round). Upon receiving it it was immediately apparent that it was imperial so I used my calipers to size the pots and glands needed. The pots needed were 2L2.5, the glands needed were 4L1.5 and the seals needed were 4L1. The cable in question was 4 core with the conductors being equivalent to 0.75mm-1mm.
When I arrived at the job this is what I found, it had been lying here like this, exposed, for about four months:
First thing's first, isolate and lock off (circuit was already off at the breaker). Then to start... I chopped the ends away with an angle grinder for a neat and square application of the stripper (a square end always makes starting off the stripper easier) and stripped back a good three quaters of a meter of the sheath with a ring and pull. Next thing to do is to get the blowtorch out and give the cable a good blasting. Short, slow even strokes towards the cut end of the cable from about 650mm back to get rid of any moisture ingress. Remember the magnesium oxide that makes up the insulating mineral compound is hygroscopic, it wicks up moisture like nobody's business! So we have to get that out.
After ten or so minutes of doing this I let the cable cool and after it was, I slid on the glands and then started stripping it back with the joistripper. This was tougher than usual as the cable was very slightly too fat to fit in the 2L2.5 hole and a bit loose in the 4L1.5 hole. I went through two blades with this bit! In hindsight I should really have used a heavy duty stripper but hey ho. When the cables were stripped back the pots were screwed on and potting compound was applied from one side only to eliminate air pockets within the pot. Notice the caps are half slid down, this helps to keep the conductors in place through the potting compound filling process. The caps were then put in place and crimped using a mineral crimping tool.
When this was done it was time to IR the conductors and copper sheath. The lowest result was roughly 20Mohms live-live. Not perfect but okay. After this I belled out the ends between the break and each lamp post with my long lead to determine which core was which and also to check earth continuity on the sheath which was being used as the cpc. Once this was done the insulation was applied and the cables identified. Two cores were not used and were disconnected at the lamp posts. At the supply end I ensured that these were earthed as they previously weren't.
Once this was done I terminated the gland at one of two Pratley underground junction boxes making sure to clean the copper on the exposed mineral sheath to ensure zero resistance between this and the olive within the compression gland. I then prepared a short length of 4 core 1mm SWA to bridge the gap and terminated this into the other side of the Pratley.
This process was then repeated on the second Prately on the other end of mineral cable so that the short length of SWA was the bridge in the gap of the break. Once this was done it was time to seal the gland terminations. I tightly wrapped some insulation tape at the join between the glands and the cable to ease the transition and then wrapped tightly and carefully with a couple of layers of self amalgamating tape. This will seal the joins and prevent corrosion of any previously exposed metal.
Once sealed up the cables were joined with wagos and the circuit tested, dead tests then live. Total lowest IR had now reduced to 15Mohms (a product of the increase in length [2x25m = 50m]), again, not perfect but okay. Pratleys have a built in method of preserving cpc continuity so no need for fly leads. All tested out ok so MCB on and a functional test of the circuit carried out. All ok. MCB off, JBs sealed up with the lids and put in place, circuit energised and away we go!
The customer was told by more than one person that it couldn't be done, and here it is! Never say never! :)
Great thread but for heavens sake DS get yerself some new trousers, a split right at the crotch! In this chilly weather and all!
:willy_nilly:
Haha, they're scruffs, the good old crotch split happens at about 6 months, I've gone through two other pairs before I decided to just not care lol. They're great everywhere else bar the crotch area, seems to be their weak point.
I think it proves the point, that there is a very big difference between the two cables, in the real world....LUL have always had their own specifications on the underground, as well as the own specifications on the fire alarm system...With Advanced fire alarm systems being the only system they will now use, being manufacture especially for LUL
just to keep the theme of old times Does anybody remember or indeed used, the crappy little modification that was brought out to try and reduce the potting procedure
It was a resin filled spacer come shroud type thing that had to be heated with a purpose made torch come oven
It never became popular or replaced the traditional method,
Ahhh the shrink on seals they were a good idea but the Pyro heatgun / oven / blowtorch thing they produced as the tooling needed was absolutely useless
When they first came out in about 1980 one of the new build Pilkington sites in St Helens was used as a test site and all the fire alarm pyro's were terminated with them. They also had an earth tail seal that was a shrink on job. Never heard of any problems and I assume they are still in place although the site was extended some years ago
They were very good for repairing old imperial pyros quickly as they would fit a number of cable sizes, when they were discontinued the pyro rep gave the company I was with at the time all the remaining stock from BICC in Prescot ( a briefcase full ) and they were slowly used up over a few years
but I would give them 1 out of ten for effort
I think a pyro terminated with a shrink seal is still a lot better than an FP cable, they could have done something better as in the early days they had a few issues with the blowtorches due to being cheap and nasty (loads were returned to BICC) and getting people to accept change (nothing new there) they were never going to be a big seller with people so used to the quality a pot termination gives. I liked them for certain things and used both pots and the shrink seals while they were available
D. Skelton good to see someone repairing a pyro rather than rip it out and a good write up too a bit of a trip down memory lane for me
If you get the job to do the upgrade, it would be interesting to find out what the IR is then. If the old seals on the other ends are tight that residual moisture might have dispersed far enough to give a nice high reading.
I always used to doubt that bit at first, where they said that even quite a low reading will come good over time as the moisture spreads out rather than being all in a ring around the end. But you only have to heat an old sheathed heating element to see how true this is. Could be megs when cold but while it's warming up the insulation drops to tens of K as all the moisture from along the length condenses around the cold ends.
Nice explanatory post there, hope it will persuade people to brush up on their MI skills.
Last week I did a job for forum member joramtor. Link to the original post here: Electrical Blog - Electrical Advice | Free Electricians Advice Forum - http://www.electriciansforums.co.uk/electricians-unite-jobs-your-area/87967-repair-micc-pyro-cable.html
View attachment 23494View attachment 23495
View attachment 23496View attachment 23497
View attachment 23498View attachment 23499
View attachment 23500View attachment 23501
View attachment 23502View attachment 23503
View attachment 23504View attachment 23505
View attachment 23506View attachment 23507
Hi are you still working with imperial micc. I have electricians saying to me just because of one strand of the micc cable has been cut that I need a new rearing job done. They say parts not available to reterminate imperial mic. This is for connection to light switch. You defo look like you know what you are doing. Where are you and can we chat please. Ime in Hertfordshire by the way. Thanks Andy.
Imperial MICC can be reterminated using metric parts, there is a conversion chart which shows which pots and seals are required.
You might have to shop around a bit to find an electrician who can do the job, but there are still a lot of us around.
MICC is classed as a specialised job these days, unbelievable it was once an everyday task for any Electrician back in the day.
Unfortunately the price of it makes it hard to justify on a job these days, a 100m drum of 2l1.5 will set you back nearly £900 and a pack of 10 glands is easily £40.
I still work with it occasionally, usually repairs or small alterations/extensions to existing MICC installs.
Certain brands of pvc coated steel flexible conduit aren't much cheaper.
Wow, I rarely use any floppy conduit, which brand?
We have used this, I think we got it a bit cheaper elsewhere:
Works out at just over £30/m ouch!
At this point I'm sure folks are thinking "WTF why use that?" but we found it lasts outdoors when flexing, while most others we tried would split after a year or so, etc.
Yes, I would struggle to think of cases where MICC is going to be your go-to choice as the traditional fire alarm case is now almost always FP200 or similar. Off the top of my head:
  • Churches and similar historic buildings where the bare copper would look the part, even if in reality the building pre-dated electricity by several centuries.
  • Blast furnace and similar where operating at seriously elevated temperatures is needed.
  • Nuclear sites (not just power stations, but some research or medical) where radiation tolerance is needed.
  • Military situations where NEMP protection is needed.
Any other suggestions?
Petrol stations
Right or wrong, that is because of the electrical trade in general and it's views regarding other cheaper and inferior methods of wiring being produced and introduced as replacements.
For the last 40 years we've been subject to so many alternatives. Ease for labour and pocket, being the main reasons why. Still nothing to rival it.
If nobody had ever seen or heard of the stuff and it suddenly came out on the market today, it would probably warrant it's own apprenticeship. 😉😊
You anywhere near Hertfordshire? I really don’t want to rewire the flat because of single strand....failing that where or how do I find the measurements of existing imperial pyro such that I can convert and get new termination kit... many thanks
Sorry about my posts, I sound like a pining teenager.. having come across all you guys I am confident I can get micc imperial repaired.. i have an electrician coming around today but over the phone he says it’s a rewire job.. and not knowing I would have taken his word... mainly him suggesting because you cannot get termination kit for imperial these days. His words.. I don’t doubt his ability at all, but I do think he has perhaps used my lack of knowledge and worry over this to make it a larger job.. I just can’t believe that because 1 single strand of the micc cable has broken near the pot that it means rewiring the flats lights... I will take some photos of the MICC connection if ok and post them, if you all don’t mind I will then ask your advice on size of pots I needs etc (imperial to metric conversion).. I’ll get it all, and then I just need someone to do it.... thanks.. glad I found this thread
There could be ways to solve your switch problem without working on the MICC.
Do you know which core is broken? Live? Switchwire?
Could you do away with the switch altogether and use a “quinetic” switch instead?
You don’t want an inexperienced electrician messibg with MICC. If this one thinks it can’t be done, he could make a hash of it.
Sorry to say, it’s definitely not a diy job
Oh totally agree. I have researched enough to see that I need someone who knows what they are doing that’s for sure. I see him in an hour so I’ll sound him out. The Quinetic switch sounds interesting I don’t know what that is but will research. I think the wire that broken is but the wire for the immediate light it operates. I think it is for the two lights that follow in bathroom and bedroom as they are not working because of it. As I say I think I can source a gland and pot and tool for that matter. Just need someone to do the job. I hate not knowing and really am in hands of professionals but don’t know if the advice they are offering is to benefit them or me. Hence I am pleased finding this forum and you guys. If you can offer any suggestions I would be very grateful. Having redecorated just and spent a fair amount getting the flat ready for sister. There’s not a lot of cash to pay for a rewire that’s for sure
Most flush MICC installs of that era I've worked on used shallow boxes which had the built in clamp to hold the pot. If that's the case here it would be quite a bit of work to get a deeper box in there to take anything other than a standard plateswitch.
It is always possible that this could be a symptom of a bigger issue and rewiring is necessary. But if it is a simple case of someone has done something to damage this one cable then it should be repairable.
Yes, post up some clear pictures so we can see exactly what has happened and get an idea of what repair is required.
Is it the MICC cable which has been damaged or is it one individual conductor within the switch box that has been damaged?
Wherabouts are you?
Licence conditions on some West end theatres still require it, or required it up until recently, which is why I'm still working with it semi-regularly.
Although with some of them it's more a case of in-house staff hanging on to old rules and refusing to keep up to date, some of them still have a fit if you dare to bring 2 phases within 6 feet of each other.
The natural history museum also specify it for all of the areas with exposed stonework. You can see some fairly recently installed MICC in there which has been done to a very low standard, nowhere near straight and no thought to aesthetics.
Some photos of the switch and connection
Do you have the front half of the pot clamp? I assume this circuit is currently isolated if the clamp is missing?
Wherabouts is the damage, it doesn't look like anything is broken as far as I can see.
If you mean the cover that goes over these two cables yes I do. I unscrewed the cover and this was what lay beneath. They are both 3 core, the right hand one you can only see two cores and the third basically snapped off so you only see two. I had an electrician around who seemed to know his stuff, I think. He said not enough left of R/H 3rd core to do anything with as too short. Said that pots etc can get online also said the cable would need to be stripped back about two foot as to ensure any moisture is taken account of. He said copper becomes brittle so no guarantee when he digs out two foot of pyro that he will be able to terminate as it may be too brittle to do so but that is a risk that I must consider. He said that it would be terminated if not brittle to a sealed junction box and then twin and earth to the light switch. The big concern was if the pyro was brittle and it could not be terminated it would definitely need a rewire. The core cable that came away was for feed to other lights in the circuit I.e. bathroom and 2nd bedroom. He said that pyro was encased by concrete and that would be a big job to trace. I guess the concern was the cable being potentially too brittle to terminate if cut back
Good, this clamp makes the earth connection to the copper cable and the circuit must not be energised without it fitted.
I can't make out the 3rd core for either of them.
Has anyone said what that thrid core is being used for?
It is very hard to make a repair if it is snapped off at the pot, but not always impossible.
Cutting back 2 feet is unnecessary, it will only need to be cut back enough to expose enough of the snapped off core to be able to join onto it.
Has anyone carried out any testing yet to see if the cable is in useable condition or not?
The only real risk is that the cable may have corroded due to chemicals in the plaster. But it looks like it is plastic coated MICC which has just had the last inch or two removed, you can see the orange outer sheath on one of them.
The sheath will have protected the buried cable from corrosion.
I keep looking at the picture and it looks like 2L1, even with the wiring configuration N's connected together in back box ? Perm Live in Common S/L out ? But hey am not there if you say 3core okay.
Silly question I take it the light/ lights dont work?
Could be a 3L1 disc but have only potted 2core
Is it just my eyes looking at a phone screen, but I count only 4 cores between the 2 cables. 2 into a connector and 2 into the switch.
If there is even a short stump of the broken core, can a small 5A connector be screwed on and extend the wire?
I haven’t made pyro off since my AM2 circ 1999 but I’m sure I still could with little issue.
I know this is not in the exam anymore, but is it still taught at college?
They look like wedge pots rather than the usual screw on pots, were they ever used on metric cable or were they older than that?
D Skelton
Mentor
Milton Keynes
Heavily Qualified Electrician / Teacher / Tutor - etc
Repairing imperial mineral cable
D Skelton,
DPG,