The customer was told by more than one person that it couldn't be done, and here it is! Never say never! :)

I'll tip my hat to you and say "well done", not something I would even consider doing .... not saying I couldn't, just wouldn't want to even go there!
 
Good work, just a shame there doesn't seem to as many out there any more who can work with MIMS, MICC, Pyro or what ever else you want to call it.

Not done many ends of it myself in 20 years but I still feel confident when I need to terminate it.
 
Used to do Pyro risers a fair bit ,about 25 to 30 years ago and the odd repair on communal lighting here and there , still got all the tools, but haven't used it for a long time now , still good job nice to see these practices in use today..
 
Nice job !
I would have gone for a one ( if the strip lengths were not to long) or two resin joints personally as I just do not trust cw's that much , but as with most stuff that's just down to personal choice .

We are just in the middle of installing a mezzy floor in our unit and only last week while emptying some of the racking to make room for the legs , I found all of our Pyro gear and tried to work out when I had last used it ! I think it was about 8 years ago on some heating controls in a school plant room that we were installing ?

I do not tend to see it now days as my other director looks after the school side , but having said that we have had two rewires so far this year in the same village where we have reluctantly replaced the original Pyro , one in the village church with FP200 and the other in an old estate house with T+E .

In the estate house all of the cables entering the metal JB's had been soldered to the casing as well .
 
Well done with the presentation.I am sure it will be very informative for anyone not familiar working with the cable and how it is made off with good step by step instruction
icon14.png



One minor tip that you practised but did not mention in the description and it is shown in your photo's

You explained how to insert the compound from one side only to minimise getting air pockets, but you did not note that you used the wrapping to cover the compound when inserting it,( not getting your mitts on the compound when filling the pot)

I therefore need to admonish you on your teaching skills,you must try harder
icon6.png

icon7.png


Again a well presented subject and carried out by a fine electrical tradesman
icon14.png
 
One minor tip that you practised but did not mention in the description and it is shown in your photo's

You explained how to insert the compound from one side only to minimise getting air pockets, but you did not note that you used the wrapping to cover the compound when inserting it,( not getting your mitts on the compound when filling the pot)

I therefore need to admonish you on your teaching skills,you must try harder

Oh yes haha! Well spotted, I completely forgot to mention it! I suppose because it just comes naturally. I shall hang my head in shame :( lol
 
Thanks for the informative post, Mr Skelton. :)

Many of the subsequent posts abouve are along the lines of, "Haven't done one of these for years." What's the reason for this? Are there cheaper, easier alternatives nowadays, for many of the situations where it would have been used routinely in the past? Is MI cable still used routinely anywhere?

Thanks again. :)
 
FP200 is now been used instead as it's easier, quicker and cheaper. micc is still used, but not as much.
 