What is the current position with installing a replacement consumer unit, where there is no c.p.c. Can the existing cable remain according to the regulations, by placing a label at the C.U. warning against fitting metallic fittings?
 
Hi - in my view the lack of a CPC should be fixed, as the circuit is a fail on the EIC ... which it can’t be, if that makes any sense.
 
My understanding is something like a CU change should result in an installation that is no worse than before in terms of compliance.

No earth for the lights was OK in the distant past (OK probably with all Bakelite fittings) but not now and it might be that rewiring to correct would cost too much for the customer so they would do nothing (no idea, just for argument here). However, having RCD protection on the lights from a new CU is a major improvement in overall safety even with no earth for the lights.

I would be far more worried by perishing rubber and/or signs of insulation failing with old cables, but not my call!
 
Best practice guide 1 the op needs to read
Regarding consumer change. Look for electrical safety first.

I guess this is the guide you mentioned?


Looks quite sensible, has section 10 on exactly this issue, worth looking over if for no other reason than protecting one's posterior. Seems the TL;DR version is:

  • See if they will get it rewired (or dedicated CPC to each accessory, probably as much trouble/cost and less elegant than a rewire), or
  • See if all light fittings can be made class II, or
  • Insulation test from L+N to each accessory's earth to make sure it is safe at that point in time (I guess including fixing screws on plastic switches?)
The guide has 1M as the lower limit for insulation tests, not sure I would be happy that low, but hey at least it ticks the box of "followed best practice" if asked!
 
Last edited:
This thread debated this subject and also the ESF Best Practise Guide. #88 I received a reply from ESF, about the conflicting advice between its flow chart & indent 10.7.

 
This thread debated this subject and also the ESF Best Practise Guide. #88 I received a reply from ESF, about the conflicting advice between its flow chart & indent 10.7.

Thanks for pointing out the thread. Seems the discussion got a bit heated at times! However, I think the main bit to take from all of that thread is one line from the reply you got:

In an ideal world we would not permit such an arrangement but instead the signatories agreed a more risk based approach.

That kind of sums up life really. Ideally no one would want 50+ year old cables without CPC for their lights but if rewiring is not an option for whatever reasons (needed quickly after damage to CU, owner can't afford it, disruption/risk to property too high, etc) then the risk-based approach is to see if it is acceptably safe and the owner agrees to the limitations then it is OK (i.e. cable not a fire risk due to perishing, no signs of insulation failing to the existing accessories).
 
Last edited:

Reply to Replacement CU and no CPC on light cct. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
468
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
561
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock