There is a way to fit a 2-module starbreaker RCCB into this, at least I managed it on an older board than yours. Crabtree technical advised me how to do this, so it is legit, though be warned that it is messy, and it may not be right for all installations.
You need a direct connection kit part number 100/DC1.
Remove the old 3-module RCD, leaving 3 newly vacated positions on the busbar, the middle being a blank (it was red on the one I did). The 100/DC1 plugs into the left position, and the new 2-module RCCB plugs into the right position, spanning across the middle position.
Now the messy bit:
Connect the line terminals of the 100/DC1 and RCCB together. Connect the outgoing neutral terminal of the main switch to the top neutral terminal of the RCCB. Connect the bottom neutral terminal of the RCCB to the neutral bar.
For this, I used 16mm meter tails. IIRC, it wasn't possible to get 25mm into the neutral bar, and was too difficult to work with anyway. Even using 16mm was a pain, and takes up a fair bit of room in the board. So your downstream circuits are limited to the 87A of the 16mm tails (not an issue if upstream fuse is 80A or less).
Technically, you could wire the neutrals to the RCCB the other way round, which takes up less space/is neater, however it leaves the RCCB with incoming line on one side of the RCCB switch, and the incoming neutral on the other. Crabtree advised against this.