I'm looking at a job in a school replacing all the light fittings for LED.
My concern is the age of the wiring.
Asi understand it, you can swap accessories without certifying (maintenance I suppose) but obviously I am swapping every single light.

So I guess my question if anyone is willing to offer advice is... Would the installation need upgrading to 17th as I am not altering any wiring, just swapping light fittings.

Thanks
 
If it's a old school then the wiring is probably MICC, in which case you have nothing to worry about as it will probably outlast us

If you're talking about notification it does not apply to schools and as said it's like for like swapping, only possible problem would be no cpcs and class 1 fittings
 
As I thought it thought I'd better check as its on a larger scale. I will push the idea of a eicr 1st I think and then we'll know what we are working with. Thanks
 
Easiest way would be test out existing circuits , if the insulation resistance is to regulation then it's passed and you can swapp fittings over
 
I think I'm going to suggest a test and take it from there. Then we can both be happy. I know its fine, they know the job won't go over budget
 
I would definately give the circuit a quick test before I started replacing fittings. At the very least, test the circuit IR and also the Zs at the furthest point.
 