Carried out an eicr and noticed x2 double sockets have reverse polarity that supply a frying machine at high level.
After correcting the reverse polarity on the two sockets i plugged the fryer back in and the circuit MCB tripped out and the appliance popped.

I am unable to open the fryer up as its fixed into the unit.

I cant seem to work out why the original appliances required the sockets to have incorrect polarity at the socket, and after correcting the reverse polarity the appliance tripped the fuse.

I checked the newly configured polarity and the sockets were correctly wired wheres before the L-N had been reversed.
 
Last edited:
Carried out an eicr and noticed x2 double sockets have reverse polarity that supply a frying machine at high level.
After correcting the reverse polarity on the two sockets i plugged the fryer back in and the circuit tripped out and the appliance popped.

I cant seem to work out why the original appliances required the sockets to have incorrect polarity at the socket, and after correcting the reverse polarity the appliance tripped the fuse.

I checked the newly configured polarity and the sockets were correctly wired wheres before the L-N had been reversed.
What tripped CB,RCBO or RCD what instrument did you use to confirm correct polarity? looks like you need to carry out some more test on the circuit supplying the 2 twin sockets
 
have you checked out the way that the cable for the fryer was wired into the frier?
 
Without the fryer plugged in the MCB stays on, i checked the plug top and it was fine.
Fault on the fryer then, diagnosing from afar. As the job was an EICR thats, an inspection of the fixed wiring, which you have found and rectified a fault, your client needs to get the fryer tested under ISITEE the new way of saying PATesting, in my opinion.
 