Discuss reverse polarity on appliance socket in the UK Electrical Forum area at ElectriciansForums.net
Carried out an eicr and noticed x2 double sockets have reverse polarity that supply a frying machine at high level.
After correcting the reverse polarity on the two sockets i plugged the fryer back in and the circuit MCB tripped out and the appliance popped.
I am unable to open the fryer up as its fixed into the unit.
I cant seem to work out why the original appliances required the sockets to have incorrect polarity at the socket, and after correcting the reverse polarity the appliance tripped the fuse.
I checked the newly configured polarity and the sockets were correctly wired wheres before the L-N had been reversed.
After correcting the reverse polarity on the two sockets i plugged the fryer back in and the circuit tripped out and the appliance popped.
What tripped CB,RCBO or RCD what instrument did you use to confirm correct polarity? looks like you need to carry out some more test on the circuit supplying the 2 twin sockets
Without the fryer plugged in the MCB stays on, i checked the plug top and it was fine.
Fault on the fryer then, diagnosing from afar. As the job was an EICR thats, an inspection of the fixed wiring, which you have found and rectified a fault, your client needs to get the fryer tested under ISITEE the new way of saying PATesting, in my opinion.
As per Westy, if the circuit is not RCD protected, there is likely an L/E fault in the fryer that was hidden, maybe deliberately, by the reverse polarity at the socket. An IR test or visual will probably find it in minutes, could be within an element. If an RCD is present, it is mildly surprising that this did not trip but doesn't change anything.
Reply to reverse polarity on appliance socket in the UK Electrical Forum area at ElectriciansForums.net
Hi all, I’m hoping you can shed some light on a problem I found. Please be gentle, I’m an industrial spark, not a domestic spark. I’ve been...
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...