and what if the circuit in question is kitchen power and 20amp isnt enough for the connected loads ?
will a 12amp drop in capacity suit the customers power requirements ?
needs more thought than that.

I believe he was being sarcastic biff...
 
You're assuming I have no evidence. You havent provided any so far.

All other circuits (2 x 2.5mm2's on 30 A MCB's) are Ring Final Circuits, so there is no reason why this one wasn't once a ring final circuit. The OP , Adam B , has at no time said there are other rings circuits in the house , so youre still making assupmtions.

All accessories I have located have 2 or 3 cables, and I know where the spurred legs go.
Are you talking about a job you've done or the posted scenario ? dont know where youre going with that statement.

I assume the original electrician installed as per the regs, and the circuit was a ring final circuit. Unless I can safely prove otherwise, the circuit(s) will remain together.
Assumption isnt proof though is it ? whereas i can prove its 2 radials by carrying out the tests i mentioned earlier.

.......................
 
.......................

Most of my comments refer to my own scenario, and I have done all the tests and investigations that I can (without ripping the building to bits).

In my experience, it is not always possible to locate the fault (if exists) or prove as two radials. This was the case with my recent scenario, and IMO the downrating of over current protective device is the best option under the circumstances.

We all have different opinions on how best to address things.

What the OP, Andy B, decides to do is his choice. As long as he is satisfied that he has done the best he can under his circumstances to address the issue.

The issuing of a Minor Cert to record the down rating will not implicate me / our company if the fault is still present and causes injury or fire (which is also unlikely due to RCD protection). I did not design or install the circuit in a dangerous manor, I have only provided better over current protection for the conductors in use.
 
Adam, why have you hi-jacked Andy B’s thread? The waters are now so muddied it’s hard to define fact from fiction.
Hopefully Andy B will re-appear and give people some solid information rather than all this conjecture.
 
Just read through this thread and seems Adam has somehow morphed into the OP somehow....made my head spin TBH.
 
was about to comment, but rockingit has posted a thread entitled cheap beer, so i'mm off over there.
 
Sorry I posted that thread last night and never checked back.

What happened was the sockets to the dining room wouldn`t reset. First thing I saw was plastic conduit running around the outside of the house fed from a socket and feeding another socket inside the house (nice). I disconnected that and found the fault still hadn`t cleared. Quite surprised that it hadn`t cleared I disconnected the sections of the rings and tested each. I eventually found the section of cable with the fault on (continuity between live and earth). I disconnected the cable at both sockets. I then put each end of the ring onto individual 20A breakers at the board. I couldn`t think of a reason not to connect it like this but thought I would ask for reassurance.
Thanks
Andy
 
That's fine, as long as you've tested the individual legs and everything's ok, and as long as the installation methods permit 20a breakers.
 
there is no problem using 2 radials as long as the loadings for the circuit are not likly to exceed the current rating of the MCB also the Zs readings are within the required values ,also you are 100% sure that the fault has been removed from the circuit a there is no hidden potential problems like multiple open circuits live missing in one socket , neutral in another , earth in another if you see what im saying , i must admit i do try and trace a fault especially one like you have described just for peace of mind
 
Adam, why have you hi-jacked Andy B’s thread? The waters are now so muddied it’s hard to define fact from fiction.
Hopefully Andy B will re-appear and give people some solid information rather than all this conjecture.

I never intended to hi-jack this thread.

I was simply offering an opinion on the issue, and using my own situation as an example to reinforce my opinion / decision. I never asked for any support or advice.

My responses were to defend my opinion, and I was using my scenario as an example to how I made my decision / opinion.

Apologies if it has been misleading, but biff55's responses were directed at my comments / opinion which is why I defended them.
 
I have just had a similar problem. I went to a customers house to install a double socket into an existing ring but on testing the ring for before carrying out the work I found the was no continuity on the L,N or E. Now ALL the sockets are working and I have identified which leg is feeding these sockets which means it can only be the last return leg back to the board. I explained to the customer what the problem is and the implications it could have but his response was "well its worked ok up until now so just leave it" as he didnt want the mess of me trying solve the issue. I put the circuit on a 20a breaker and told him I was unable to install a new socket until this problem was fixed.
 