I have seen things like this before, I have also seen the opposite where 2.5 steps down to 1.5 in a ring.
When I took the cover off the CU I thought that someone had piggy backed a light circuit onto a power circuit!!

Until I took off some socket faces to find some 1.5mm looping - The customer would not pay for it to be changed and would not let me downrate the MCB so I made a note on the cert for the shower I installed and left.

I think the guy thought I was sniffing for extra worked and was making it up, same old saying. Its work for 10yrs mate.

I just hope that one day if his heating breaks that he does now plug a few 2-3KW heaters in!
 
Thanks for that Eng, but it did occur to me at the time, was the first thing I checked! The CPC is solid core. I have encountered some 7 stranded T&E before which appeared to be aluminium coated with copper....was awful stuff, brittle as hell. I remember then initially thinking it was 4mm, but fused it at 20a at the DB cos I didn't trust it! :)


The old imperial 7/029-7/036 is a far superior cable than the solid 2,5mm cable we have today, also has a better CCC!! In fact, all the solid core cables should be stranded. It'll make for far easier pulling in and final dressing is a breeze!! lol!!! All our conductors on this project are stranded, so it's not as if manufacturers don't make/produce stranded 2.5mm...


The cable you are referring too is ''tinned copper'' conductors, not aluminium coated copper. Never seen a brittle tinned copper conductor just over worked conductors. Probably more a case of you not being experienced/used to smaller stranded conductors. Plus the more you work any copper conductor or copper sheath, it will harden and snap...
 