Following on from another thread I have just replied to it got me thinking about ring circuits and reference methods.
Appendix 15 shows a ring on a 32A MCB. It does begin with a get out clause regarding thermal effects but it just points you Chapter 42 which deals with fire.
If for example we had a ring which was completely routed in reference method 103 what MCB would we choose? We know that the CCC of 1 x 2.5mm cable is 13.5A but how does this tell us exactly what size MCB to use for the ring?
There must be a simple equation to use based on the CCC of 2 x 2.5mm cables used as a ring, to find out the MCB required?
Hi - I haven’t seen any regulation or guide values for RFC outside of “20A minimum ccc for 32A mcb”, but I’m always happy to learn. Design wise the factor would appear to be 1.25 ... ie I assume someone has tested (by long experience perhaps) that 2 x 20A won’t be damaged if protected by a 32A mcb (40/32 = 1.25). So 2.5 floating in stud wall with insulation (method 103) might be protected by 2 x 13.5 /1.25 = 21.6A mcb, ie 20A . Just my thoughts :) .
3/4 of the combined CCC of the two legs.
Interesting...
So with your example Wilko 2 x 20A would be fine on a 32A MCB but not with SL's (i.e 40 x 0.75 = 30A)
Two electricians who know their stuff but 2 different ideas. That's why I'm asking as there doesn't seem to be a definitive answer. I'll be interested to see more replies!
The loading is deemed to be 20 amp at the furthest or mid point with a further 12 amps evenly distributed around the other leg of the ring hence 20 amp minimum for the Iz of the cable is required for compliance with 433.1.1 Overload protection for a 30 or 32 amp ring final circuit
The method Wilko is probably the more modern method, using 32A instead of 30A.
40 divided by 30 = 1.333.
2 x 13.5 / 1.333 = 20.25A.
Reply to Rings, reference methods and CCC... in the UK Electrical Forum area at ElectriciansForums.net
  • Locked
5K
The garage is 17 mtrs x 15 mtrs in the UKh The house has a 100 amp supply to the house consumer unit. The garage consumer unit is fed from a...