Legend, this might be the answer!If you want them with a cable tie hole it's a britclips BC125 these will also go on a 2mm purlin with the hole over it.
Sy
Legend, this might be the answer!If you want them with a cable tie hole it's a britclips BC125 these will also go on a 2mm purlin with the hole over it.
Sy
Sorry missed that
There will probably be an initial run of 8-10 cables so im not sure whether girder clips would be the best option
Ive only ever done it after a roof is on, and no ceiling is being fitted, ie its all left exposedI see and have put cables in purlins as you describe, but its never the first choice. If the cables are inside the purlin you are only one screw away from cable damage if a roofer or cladder come along. You would be surprised how long the screws used by roofers can be. "Why use a 2 inch screw when i have a couple of hundred 4 inch screws", lol -
If i was planning from scratch i would use my own containment, see it as an investment for the future
I am referring to subsequent cladding and roofing upgrades to insulated roofs, i have had it on two buildings where repairs / upgrades have damaged cables (not ones i have installed, i might add...Ive only ever done it after a roof is on, and no ceiling is being fitted, ie its all left exposed