Hi people,
This is just a question!

I was wondering how to go about putting a separate consumer unit for a garage.

Could i run the main supply to a henley block, then split from there to the main CU and then from the henley block to the garage CU. problem is that the garage is about 10m from main CU.

Just wondering what your views were
 
Hi Lee.
This is just an answer!

Lots of variables to consider but the bare bones of what you're proposing is OK, perhaps not the way I'd do it but without a lot more info.......
 
why not just come out of the upstream board with an armoured....
i mean, whats the earthing arrangements for a start....
and how do you propose to protect them tails feeding this garage....
 
Could i run the main supply to a henley block, then split from there to the main CU and then from the henley block to the garage CU. problem is that the garage is about 10m from main CU.

no you cant do it like this , otherwise the swa cable to the garage is only protected by the dno fuse as youre by-passing the house CU.
if no spare way in CU then standalone switchfuse for the swa.
if youre confused by the above terminology best call a professional ;-)
 
I was thinking SWA from the henley. Its mostly surface layed with about a 1m length under a path way. Its a TN-S supply, thinking met next to henley?

There is a Sparky doing it (havent met him) this is me trying to get it in my head.
 
Well, come 9am tomorrow you can talk to the technical help line of your scheme. They don't bite.

Hold on, one of your earlier posts you said you were a spark.
 
There is a Sparky doing it (havent met him) this is me trying to get it in my head.

then why bother asking advice if youve someone to design it for you ?

that would be like me trying to work out water flow rates of a new heating system even though a plumber is doing the job for me
let him do it , thats what i'm paying him for.
 
Trainie spark. Left the army and retrained. Theres a lot to learn. Didnt feel comfortable with this. But was still interested in how its going to be done. Wont be able to get round there till its done so was asking to see how others would do it.
 
Trainie spark. Left the army and retrained. Theres a lot to learn. Didnt feel comfortable with this. But was still interested in how its going to be done. Wont be able to get round there till its done so was asking to see how others would do it.
Lee...
see what the electrician says when he turns up tomorrow.....
but i can tell you now that an armoured would be the way here......
 
Needs fused down Lee to below the rating of the cable, before it leaves the house heading for the garage.
Straight out the Henleys isnt an option.
 
Hi Lee.
This is just an answer!


Lots of variables to consider but the bare bones of what you're proposing is OK, perhaps not the way I'd do it but without a lot more info.......


Ha ha, I like it!
 